The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
51 minutes 42 seconds ago
International Wire Colour Codes
by Tjia1981
Today at 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 7
renosteinke 6
ghost307 6
Potseal 4
Who's Online
0 registered (), 277 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#61316 - 01/21/06 05:39 AM arcing ground connection
sandro2 Offline

Registered: 03/26/05
Posts: 49
Loc: philadelphia,PA
I went to a house and at the cold waterpipe the ground was arcing against the water pipe.
I checked the neutral at the tap,meter socket and panel all were tight and made sure the neutrals and grounds were tight inside the panel. I tightened the ground connection and it stopped what could be the cause?

Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#61317 - 01/21/06 05:42 AM Re: arcing ground connection
iwire Offline

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
The problem was a loose connection at the water pipe.

The 'cause' is required by the NEC.

The bonding of multiple services to a common underground water pipe results in current being carried on the water pipes.
Bob Badger
Construction & Maintenance Electrician

#61318 - 01/21/06 06:22 AM Re: arcing ground connection
sandro2 Offline

Registered: 03/26/05
Posts: 49
Loc: philadelphia,PA
Thanks I just wanted to make sure I wasn't overlooking anything. I ran into this problem once before and it was a losse neutral at the taps along with alittle loose on the water pipe.

#61319 - 01/21/06 07:06 AM Re: arcing ground connection
Rewired Offline

Registered: 01/01/06
Posts: 567
Loc: Hamilton, Ontario, Canada
I have seen grounds carry current even with the mains to the house open!
Sometimes your ground connection is a path for current should one of your neighbours say have a bad or open neutral somewhere in their service..

#61320 - 01/21/06 08:14 AM Re: arcing ground connection
HotLine1 Offline


Registered: 04/03/02
Posts: 6792
Loc: Brick, NJ USA
A posibility also could be a 'bad' neutral connection on the utility side. Had that quite a few times, both OH & BUD.


#61321 - 01/21/06 03:16 PM Re: arcing ground connection
LK Offline


Registered: 01/21/03
Posts: 1721
Loc: New Jersey
Just came back from job plumber left and told homeowner to call electrician, we found loose neutral at service head, cut back. and cleaned, new bug, and we hope the plumber will return.

#61322 - 01/21/06 06:13 PM Re: arcing ground connection
jdevlin Offline

Registered: 08/07/02
Posts: 402
Loc: welland ontario canada
Bad neutral at a neighboring property could be putting current onto the water pipe and back out your client's neutral.

#61323 - 01/22/06 11:24 AM Re: arcing ground connection
winnie Offline

Registered: 09/15/03
Posts: 652
Loc: boston, ma
Check for a bad water heater element or another high resistance ground fault. A high resistance ground fault can cause significant current flow and power consumption, without tripping a breaker.

After you tighten the ground connection, it is worth putting a clamp meter on the GEC and flipping breakers to see if some particular circuit is causing the current flow.