The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
Yesterday at 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
0 registered (), 228 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#61255 - 01/20/06 04:27 AM Residential Service
sandro2 Offline
Member

Registered: 03/26/05
Posts: 49
Loc: philadelphia,PA
A 200 amp residential service with the Pipe installation inside of the home?
-needs to be encased in concrete
-Can the pipe be EMT?
-Also what is the disconnect rule as far as the distance of the pipe before installing a disconnect

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#61256 - 01/20/06 07:16 AM Re: Residential Service
electricman786 Offline
Member

Registered: 09/17/04
Posts: 37
Loc: sacramento
Y dont u use pvc if u going 2 encase it in concrete.

Top
#61257 - 01/20/06 07:55 AM Re: Residential Service
raider1 Offline
Member

Registered: 07/08/05
Posts: 46
Loc: north logan, utah, US
If you are talking about the service entrance conductors, then you must meet the requirements of 230.6 to be considered outside of the building.

EMT can be installed in concrete if 358.10(B) is meet.

230.70(A)(1) says "inside nearest the point of entrance of the service conductors." Only the AHJ can determine what is "nearest the point of entrance." Some AHJ have allowed 5 feet but you will want to check with your local AHJ.

Chris

Top
#61258 - 01/22/06 01:54 AM Re: Residential Service
e57 Offline
Member

Registered: 05/27/03
Posts: 2837
Loc: S.F.,CA USA
This is one of the widest varying regional items around. Some AHJ allow nothing inside, some allow no encasement for 40'+! Really depends on where you are, and what is allowed there. This is definatley a question for your local inspector, and POCO.
_________________________
Mark Heller
"Well - I oughta....." -Jackie Gleason

Top
#61259 - 01/22/06 08:48 AM Re: Residential Service
Celtic Offline
Member

Registered: 02/26/05
Posts: 367
Loc: NJ
My AHJ will allow 5' inside...I have a situation where I need 8' and I don't want to put in a meter main stack. The AHJ will allow my installation ONLY if the entire load side of the meter is RGC ~ no concrete required.

You will get varying details from people.

Your best bet is to ask the AHJ that is inspecting (another AHJ - even if the same jurisdiction - *might* not allow what the other agrees to).
_________________________
~~ CELTIC ~~
...-= NJ =-...

Top