A lot of the rules pertaining to working in live panels have to do with "fingersafe" devicess. But what exactly is a fingersafe device when it pertains to the NFPA and OSHA.

I believe it would be important to be able to determine immediatlely whether a device is fingersafe or not.

How big can the hole be on the terminal screwdriver... 1/8", 1/4" or what?
Top
Work Gear for Electricians and the Trades
#61230 - 01/19/06 06:29 AM Re: Fingersafe devices and NFPA, OSHA
Mike Wescoatt Offline
Member
Registered: 06/17/01
Posts: 161
Loc: Cedar City, Utah
As far as IP classification fingersafe (IP2x) is protected against objects over 12mm in diameter. Is there a NEMA equal other than calling it NEMA-1 or better?
_________________________
Mike Wescoatt
Top
#61231 - 01/19/06 10:14 AM Re: Fingersafe devices and NFPA, OSHA
C-H Offline
Member
Registered: 09/17/02
Posts: 1497
Loc: Stockholm, Sweden
A few zealous inspectors (industry) carry around a "test finger" to verify that a finger can't reach any live parts.
http://www.ergonomicsusa.com/accJFP15.html

[This message has been edited by C-H (edited 01-19-2006).]
Top
#61232 - 01/19/06 12:24 PM Re: Fingersafe devices and NFPA, OSHA
mshaw Offline
Member
Registered: 01/11/06
Posts: 44
Loc: Fairborn, Oh, USA
I had a test finger once but my foreman took it away, guess he did not like how I applied it
Top
#61233 - 01/19/06 03:05 PM Re: Fingersafe devices and NFPA, OSHA
JBD Offline
Member
Registered: 07/12/01
Posts: 599
Loc: WI, USA
I don't think NFPA70E (and therefore OSHA) recognizes the term finger safe for 480V work. Table 130.2(C) says the restricted approach boundry for 480V is 1". Anything closer is considered making contact with the live part.

So finger safe terminals would help for the 50-300V "avoid contact" boundary but they would need to have a 1" recess for 480V.

NFPA79 6.2.2.1 address the dimensions and (proper) use of the "test" finger.
Top

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (gfretwell), 54 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals