The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
2 registered (NORCAL, sparkyinak), 205 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#61197 - 01/18/06 06:19 PM AFCI problems
BigB Offline
Member

Registered: 03/31/04
Posts: 727
Loc: Tucson, AZ USA
I did a search but didn't see anything on Square D AFCI's. I installed two yesterday, I tested first with Wiggy from H-N, everything ok, breakers held, then from H-G, breakers tripped as expected.

Today homeowner calls, they installed their own paddle fan, they said it trips the AFCI. They also said when they try to use a lamp on either circuit, AFCI trips. I can't go there for a few days, but I seem to remember a recall on Square D AFCI's.

Of course maybe they messed up on the fan and maybe the lamp is arcing or grd fault, I won't know till I get there. I know I didn't mix up the neutrals, besides, if I did then wouldn't the Wiggy have tripped them from H-N?

Any info would be appreciated in regards to what to look for. I have installed dozens of Cutler Hammer AFCI's with no problems.

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#61198 - 01/18/06 07:31 PM Re: AFCI problems
Ryan_J Offline
Moderator

Registered: 08/19/03
Posts: 1355
Loc: West Jordan, Utah, USA
The recall that you speak of was not because the breakers were tripping, it becasue they were afraid they would not trip.
_________________________
Ryan Jackson,
Salt Lake City

Top
#61199 - 01/20/06 04:49 AM Re: AFCI problems
sandro2 Offline
Member

Registered: 03/26/05
Posts: 49
Loc: philadelphia,PA
I ran into a problem w/these breakers everytime i turned on the lites in a bedroom the breaker would trip.
-make sure the wirenuts are tight that was the cause for me.I guess there was just enough arcing that that would cause the trip. I didn't think these brakers were supposed to detect arcing in the hot wire.
-I would make sure the switches are not back stabbed instead wrapped around the screw.

Top
#61200 - 01/20/06 08:14 AM Re: AFCI problems
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
"Installed a paddle fan"

Take a look at the wirenut with the neutrals in it. I bet there is bare wire showing that is shorting to the box or hickey.
_________________________
Greg Fretwell

Top
#61201 - 01/20/06 02:38 PM Re: AFCI problems
sawdust454 Offline
Member

Registered: 03/20/05
Posts: 19
Loc: Waynesboro, Va USA
Check for a connection between the grounded and grounding conductor,that will cause the AFCI to trip. Probably in the homeowner installed paddle fan.
Good luck.
Ron M

Top
#61202 - 01/20/06 04:59 PM Re: AFCI problems
HCE727 Offline
Member

Registered: 11/11/05
Posts: 190
Loc: Delaware County, PA, USA
Go to esfi.org, click on news,then product recall. You will find the Square D Arc-Fault recall.
_________________________
Hank

Top
#61203 - 01/20/06 05:03 PM Re: AFCI problems
Trick440 Offline
Member

Registered: 08/15/05
Posts: 248
Loc: Waterford, MI, USA
Definately look for all the obvious arc faltf trouble shooting.

We have had small nicks in the wires from utility knifes. The AFCI held fine, but then ever you put it under a load, like turning on the light.. It would trip.

Hopefully its an obvious homeowner mistake in the fan.... or the fan its self is bad.

Might wanna hook a different light up there and see if it trips then. If it does then probable a bad fan.
_________________________
Shake n Bake

Top