What exactly is required when mixing voltages, ie. 208 & 277 in the same J-Boxes and conduits.
As far as labeling, color codes etc.
I know what is preferable, but what is required by code.
Thanks in Advance.
Top
Work Gear for Electricians and the Trades
#61144 - 01/17/06 05:52 PM Re: Mixing voltages, marking requirements
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5316
Loc: Blue Collar Country
They need to be separated by a non-conductive barrier.
Top
#61145 - 01/17/06 05:59 PM Re: Mixing voltages, marking requirements
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
No barrier is required unless two devices in the same box have more than 300 volts between them.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#61146 - 01/17/06 06:50 PM Re: Mixing voltages, marking requirements
electure Offline


Member
Registered: 12/24/00
Posts: 4259
Loc: Fullerton, CA USA
.....And at least one of those devices is a snap switch
Top
#61147 - 01/17/06 08:16 PM Re: Mixing voltages, marking requirements
JoeTestingEngr Offline
Member
Registered: 11/04/05
Posts: 781
Loc: Chicago, Il.
Don't all of the conductors have to have an insulation rating appropriate for the highest voltage used?
Joe
Top
#61148 - 01/19/06 06:17 AM Re: Mixing voltages, marking requirements
electure Offline


Member
Registered: 12/24/00
Posts: 4259
Loc: Fullerton, CA USA
Yes, they do.
All of the Building Wire that I'm accustomed to working with has insulation rated at 600V, so it would qualify for highground's original query.

Now my question:
What is the insulation rating of Cat5/Cat6 etc. cable?
How about Bell Wire/Thermostat Wire?
Top
#61149 - 01/19/06 10:42 AM Re: Mixing voltages, marking requirements
mxslick Offline
Member
Registered: 10/24/04
Posts: 803
Loc: Atomic City, ID USA
Quote:
Now my question:
What is the insulation rating of Cat5/Cat6 etc. cable?
How about Bell Wire/Thermostat Wire?


Most CAT5/6 I've seen is rated at 300 volts. I'll check back on the new CAT6 I just used on a job, it's in the warehouse...

I've seen t-stat wire at both 150v and 300 volts. Not sure about bell wire.

Anyone? Anyone? Bueller? Bueller?
_________________________
Stupid should be painful.
Top
#61150 - 01/19/06 11:19 AM Re: Mixing voltages, marking requirements
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
Quote:
What exactly is required when mixing voltages, ie. 208 & 277 in the same J-Boxes and conduits.
As far as labeling, color codes etc

See 210.5 in the 2005 NEC.
Don

the code section should be 210.5(C)

[This message has been edited by resqcapt19 (edited 01-19-2006).]
_________________________
Don(resqcapt19)
Top
#61151 - 01/19/06 11:22 AM Re: Mixing voltages, marking requirements
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
Quote:
What is the insulation rating of Cat5/Cat6 etc. cable?
How about Bell Wire/Thermostat Wire?

Then you have to look at 725.55(A). Even if the communications and controls cables have a voltage rating higher than that of the power conductors, you still can't mix them in the same raceway.
Don
_________________________
Don(resqcapt19)
Top
#61152 - 01/22/06 10:18 AM Re: Mixing voltages, marking requirements
Tom H Offline
Member
Registered: 01/31/05
Posts: 74
Loc: Milford, Ct, USA
725.55(D) allows for mixing voltage class wires so long as the class 2 wires pertain to a device in that box. A nice one for lighting control systems.
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
2 registered (Admin, sparkyinak), 74 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals