#61140 - 01/17/06 01:14 PM 400A Disconnect ahead of CT
NJ_WVUGrad Offline
Member
Registered: 01/17/06
Posts: 47
Loc: Neptune, NJ, USA
Installing a 400A CT which is tapped out of a Trough feeding 3 other services (wireless telecom site - each carrier has a trailer).
The trough is fed UG from a pole mounted transformer.

PoCo (JCPL in North NJ) is requiring a 400A disconnect ahead of the CT cabinet so they can work on CT's without shutting off service to the whole site.

I explained that the other services all have 8hr of battery backup (which is true) and shutdown would not effect them. Yet they still insist on the 400A Non-Fused Disc.

It burns me because its not outlined in their Electrical Service Manual and the fact that it is being installed for their convenience. I assume they will be sealing it themselves to prevent tapping unmetered.

Has anyone run into this or similar?
Top
Work Gear for Electricians and the Trades
#61141 - 01/17/06 02:06 PM Re: 400A Disconnect ahead of CT
shortcircuit Offline
Member
Registered: 06/27/04
Posts: 608
Loc: massachusetts
Cold sequence for a CT cabinet is required by my local POCO also. They want the option to kill the power for servicing...

shortcircuit
Top
#61142 - 01/17/06 02:52 PM Re: 400A Disconnect ahead of CT
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6776
Loc: Brick, NJ USA
NJ:
JCP&L & PSE&G require cold sequence in 'certain' installs. It's always a "GOOD POLICY" to speak to the wiring inspector/field engineer before you do any job.

Yes, they have requirements for the 'main' enclosure to be sealable, as it is ahead of the meter, and can be considered 'access' to unmetered power.

John
_________________________
John
Top

Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (gfretwell), 90 Guests and 11 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals