I work at a utility. We got called out on a customer complaint to a grocer who had burned up his 3 phase motors.

His service was a 120/240 volt open delta secondary fed from two phases of a 4 wire wye, 12.5/7.2 Kv primary.

When we got there, we read across the "lighting" legs and got 120 volts from A to neutral and 120 volts from B to neutral. A to B read 240 volts, as did B to C.

So far so good. So.....

A to C read 480 volts (instead of 240) and C to neutral read 360 volts (instead of 208).
Neither transformer fuse was blown.

Hint: There had been many outages due to storms a few days before and lots of backfeeding had been going on.
Top
Work Gear for Electricians and the Trades
#61108 - 01/16/06 07:12 PM Re: Another brain teaser....480 on a 240 volt delta
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
Did the transformers end up on the same input phase?
_________________________
Greg Fretwell
Top
#61109 - 01/16/06 07:14 PM Re: Another brain teaser....480 on a 240 volt delta
WFO Offline
Member
Registered: 09/03/05
Posts: 202
Loc: Cat Spring, TX
Dammit! Dammit! Dammit!
Didn't even get past the first guy.
Top
#61110 - 01/16/06 07:15 PM Re: Another brain teaser....480 on a 240 volt delta
caselec Offline
Member
Registered: 04/14/02
Posts: 558
Loc: San Jose, CA
I don’t know what back feeding has to do with this but you can’t feed a three phase transformer bank with only 2 phases. By feeding both transformers from the same two phases your secondaries are connected in series giving the voltages you see.

Curt
_________________________
Curt Swartz
Top
#61111 - 01/16/06 07:17 PM Re: Another brain teaser....480 on a 240 volt delta
caselec Offline
Member
Registered: 04/14/02
Posts: 558
Loc: San Jose, CA
I’ve got to learn to type faster.
_________________________
Curt Swartz
Top
#61112 - 01/16/06 07:44 PM Re: Another brain teaser....480 on a 240 volt delta
WFO Offline
Member
Registered: 09/03/05
Posts: 202
Loc: Cat Spring, TX
Quote:
"I don’t know what back feeding has to do with this but you can’t feed a three phase transformer bank with only 2 phases. By feeding both transformers from the same two phases your secondaries are connected in series giving the voltages you see."

Right on the second half.
You CAN feed a 3 phase open delta bank with only two phases and neutral. I didn't mean to give the impression that they were going phase to phase on the primary with the common floating. The common is bonded to the neutral.

Quote:
"I’ve got to learn to type faster."

Indeed. The second response was going to win a brand new Porsche.

...oh, wait. I was the second response.
Top
#61113 - 01/16/06 10:08 PM Re: Another brain teaser....480 on a 240 volt delta
mxslick Offline
Member
Registered: 10/24/04
Posts: 803
Loc: Atomic City, ID USA
Oh, man lookit what I started....
_________________________
Stupid should be painful.
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 43 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
KrmtFrg, Stack, Scotto, Freecrowder, clee512

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals