The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
Today at 02:39 AM
Photo Upload Tutorial
by DanK
Yesterday at 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
0 registered (), 109 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#61041 - 01/15/06 07:05 PM Feeder Tap
master66 Offline
Member

Registered: 04/18/02
Posts: 260
Loc: Masontown, PA, USA
I'm trying to apply one of the tap rules and I just want to make sure I'm doing it correctly.

Here is the situation. Working on the 8th floor of an 8 story office building. There is a 1600 amp 120/208v buss duct running vertically up a chase that is tapped and metered to feed each tennant space as needed.

The drawings show a 400A disconnect being installed to tap the buss duct. The disconnect will be fused at 350 amps.

The problem is, there is no room to install another disconnect and meet all working space clearances.

So, I was thinking that I could install a tap box on the buss and run a feeder to the office space behind the buss where a new closet will be built to house the new electrical equipment.

I will first have to go through a meter then to a fused disconnect. All wiring will be installed in EMT or greenfield.

I know that I won't be able to do this within 10 feet so I am trying to apply the 25' tap rule.

If I am reading 240.21(2)(3) correctly. I can do this if I tap the buss with parallel 300MCM to the disconnect.

Am I correct or can I parallel smaller conductors in this situation.

This is the first time that I ever encountered this situation.

Thanks,
Brian

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#61042 - 01/15/06 08:22 PM Re: Feeder Tap
Bob Offline
Member

Registered: 02/05/02
Posts: 182
Loc: Mobile, AL, USA
240.21B2 requires that the conductor capacity be equal to at least 1/3 of the OC rating. 1600 x 1/3 = 528 amps. 2 #300 at
285 amps = 570 amps. It appears that you have met the requirements of B2 1,2 and3.

Top
#61043 - 01/16/06 02:55 AM Re: Feeder Tap
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
 Quote:
I will first have to go through a meter then to a fused disconnect.


That will be a problem.

 Quote:
240.21(B)(2)(2) The tap conductors terminate in a single circuit breaker or a single set of fuses that will limit the load to the ampacity of the tap conductors. This device shall be permitted to supply any number of additional overcurrent devices on its load side.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top