#60949 - 01/13/06 05:59 PM A meter bank that holds 3?  
Trick440  Offline
Member
Joined: Aug 2005
Posts: 248
Waterford, MI, USA
Do they make meter banks that hold 3 meters?

I have a house that was turned into a 3 unit apartment.

I was planning on using a 3 meter disconnect bank. Then going with main lug sub panels. but... .

The dryers and ranges are all old 3 wire. If I run sub fed panels I will need to upgrade these old wires. I really don't want to do that.

So I need just regular meters. I know the electric company has dual meter cans for 1 drop but I havent seen 3 meter, cans for 1 drop. .. Do they make something like this?


Shake n Bake

Work Gear for Electricians and the Trades

#60950 - 01/13/06 06:25 PM Re: A meter bank that holds 3?  
Rewired  Offline
Member
Joined: Jan 2006
Posts: 558
Hamilton, Ontario, Canada
I believe they do. an " SDC-320-PW" I believe is a Hydell 3 gang base, 200A main, 100 A per position with a " wiring compartment" for use with O/H or U/G feed..
This is a straight meter socket with no disconnects built in, I have never seen one like that. If you need to have a form of disconnect outside, you may need a separate weatherproof disconnect for each service going in the bldg..

A.D


#60951 - 01/13/06 06:50 PM Re: A meter bank that holds 3?  
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
I would hope that they still did!

Around here, it is quite common to see three meters, arranged vertically, with a lower compartment tht contains a disconnect/ main breaker for each service.

The only "fly in the ointment" is that these generally have 70 amp breakers; I am not sure that such equipment is suitable for 100 amp service, which is the minimum these days.


#60952 - 01/13/06 09:34 PM Re: A meter bank that holds 3?  
Celtic  Offline
Member
Joined: Feb 2005
Posts: 361
NJ
http://www.tyett.com/images/panelbox.jpg

..you mean like this?

For a 3-family, you *may* need a 4th meter - for the house/common power. Check with your AHJ about this, some areas have this requirement - some don't.


What you "want", may not be what's "required". In NJ, a substantial renovation like the one you describe (re-zoning, over 50%, etc) might trigger a complete renovation requirement.

[This message has been edited by Celtic (edited 01-13-2006).]


~~ CELTIC ~~
...-= NJ =-...

#60953 - 01/13/06 10:39 PM Re: A meter bank that holds 3?  
Trick440  Offline
Member
Joined: Aug 2005
Posts: 248
Waterford, MI, USA
Yep Celtic that what I need.

Thanks for the help guys. I did talk with the inspector and took care of all his concerns inside already.. hes ok with the no house panel.


Shake n Bake


Member Spotlight
richard
richard
L.I. New York
Posts: 94
Joined: August 2003
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.011s Queries: 14 (0.002s) Memory: 0.7662 MB (Peak: 0.9034 MB) Zlib enabled. Server Time: 2017-03-29 17:11:34 UTC