The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Correct rotation, wrong sequence
by Potseal
Today at 03:14 PM
Industrail Control Panel bonding per 409.108
by sparkyinak
Yesterday at 06:29 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 11
HotLine1 10
Potseal 9
sparkyinak 8
Texas_Ranger 7
Who's Online
0 registered (), 215 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#608 - 02/12/01 10:16 PM What would you expect?
sparky66wv Offline
Member

Registered: 11/17/00
Posts: 2339
Loc: West Virginia
A 20A 2 pole breaker has a load of 40 Amps line to ground on one side only. What amount of time should the breaker trip at twice it's rated load?

Several seconds is expected to reduce nuisance tripping on motor-start-up loads, but what would be considered extreme on the high end?

How fast would a 20A fuse blow under 40 Amps?

A time delay 20A fuse under 40 Amps?

At what percentage should a breaker trip within one minute? 120%? 150%? 200%?

Is there any info out there that may give me the data of what UL expects from a breaker or fuse?
_________________________
-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#609 - 02/13/01 07:59 AM Re: What would you expect?
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
Sparky,
You need to find the time-current curve for the device that you are using. The only one that I could find this morning for a 15 amp FRN-R fuse. It shows that this fuse will hold on average for 90 seconds at 20 amps, 30 seconds at 30 amps, and 2 seconds at 60 amps.
Other fuses and breakers will have different curves.
Don(resqcapt19)
_________________________
Don(resqcapt19)

Top
#610 - 02/13/01 08:57 AM Re: What would you expect?
sparky66wv Offline
Member

Registered: 11/17/00
Posts: 2339
Loc: West Virginia
I guess what I'm after are time current curves for:

FPE 2 pole 20 A
FPE 1 Pole 20 A (If it differs)
GE 2 Pole 20 A
SQD 2 Pole 20 A

If the hard data already exists, it will save me a lot of time. I've got the data from my own experiments, but I have a rather "noisy" lab.

I'll let you guys know what I found out, but I want to know your opinions (and any hard data you may know of) first.

You may be surprised!

[This message has been edited by sparky66wv (edited 02-13-2001).]
_________________________
-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI

Top
#611 - 02/13/01 01:54 PM Re: What would you expect?
Tom Offline
Member

Registered: 01/01/01
Posts: 1069
Loc: Shinnston, WV USA
I looked at a curve for a SQ D 2 pole 50 & it shows a one minute trip at about 130%.

As Don pointed out, each breaker by each manufacturer will have it's own trip curve. You could probably contact UL to find out what they expect, but they would probably have to sell you the standard & they're usually expensive.
_________________________
Few things are harder to put up with than the annoyance of a good example.

Top
#612 - 02/23/01 11:53 AM Re: What would you expect?
sparky66wv Offline
Member

Registered: 11/17/00
Posts: 2339
Loc: West Virginia
In a nutshell... here are the results of my, uh..."tests"...

Single Pole 20A Breakers FPE on a 40A load to ground tripped between 38 and 74 seconds.

Double pole 20A Breakers FPE on a 40A load to ground tripped between 45 seconds and well over one minute (90+ sec). One breaker failed to trip after two minutes at 200% load. The 30 Amp SQ D Breaker upstream tripped instead, within 2 minutes at 150% load.

A SQ D 20A Breaker 2 Pole tripped within 20 seconds at 40A.

The 20 Amp breakers were the only ones I could test "safely". I had no idea it would take 200% to trip them in less than a couple of minutes. You should have seen me trying to find every high current device in the house to get these things to trip. Toasters, Coffee Pots, Blow Dryers, Heat Guns, Shop Vacs, etc. etc. Scared the cats...

I had it on two GFCI 20A receptacles. But even the #12 feeding them didn't get terribly warm, at double their "rated" current.

By the way, my wife is a nurse and is here when I do these crazy things... Wait 'til I get my Tesla Coil up and running!
_________________________
-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI

Top
#613 - 02/23/01 04:53 PM Re: What would you expect?
Tom Offline
Member

Registered: 01/01/01
Posts: 1069
Loc: Shinnston, WV USA
'66

I'd like to be the first to congradulate you on getting any FPE breaker to trip under any condition. I've met quite a few electricians who feel that an FPE breaker that trips out is in the realm of an urban legend.

[This message has been edited by Tom (edited 02-23-2001).]
_________________________
Few things are harder to put up with than the annoyance of a good example.

Top
#614 - 02/23/01 05:59 PM Re: What would you expect?
Bill Addiss Offline
Member

Registered: 10/07/00
Posts: 4196
Loc: NY, USA
'66

You must be in the Smoky Mountains?


(Joke)

Bill

Top
#615 - 07/01/01 04:46 AM Re: What would you expect?
C.Urch Offline
Member

Registered: 05/23/01
Posts: 36
Loc: Kill Devil Hills, NC USA
I've cut live wires in two during remodels( by accident of course )frying my Kleins only to have a 20 Amp stab-lok breaker laugh in my face.

Top
#616 - 07/01/01 06:56 AM Re: What would you expect?
Joe Tedesco Offline
Member

Registered: 10/07/00
Posts: 3325
Loc: Boston, Massachusetts USA
Look here for more! www.stargroup.com

[This message has been edited by Joe Tedesco (edited 10-06-2001).]
_________________________
Joe Tedesco, NEC Consultant

Top
#617 - 07/01/01 07:19 AM Re: What would you expect?
Joe Tedesco Offline
Member

Registered: 10/07/00
Posts: 3325
Loc: Boston, Massachusetts USA
www.joetedesco.com

[This message has been edited by Joe Tedesco (edited 04-26-2003).]
_________________________
Joe Tedesco, NEC Consultant

Top