The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Live Chat Feature
by Admin
01/19/17 09:52 PM
Safety at heights?
by gfretwell
01/19/17 07:16 PM
failed home inspection.
by gfretwell
01/19/17 07:03 PM
Webmaster > Admin
by Admin
01/19/17 05:49 PM
Old Bath Fan
by gfretwell
01/19/17 01:38 AM
New in the Gallery:
Desk-mounted "power-board"
Top Posters (30 Days)
Admin 33
HotLine1 21
Ruben Rocha 16
gfretwell 15
Trumpy 13
Who's Online
2 registered (Ruben Rocha, gfretwell), 0 Guests and 185 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#60791 - 01/10/06 03:22 AM Cable Fault location
RODALCO Offline
Member

Registered: 12/08/05
Posts: 865
Loc: Titirangi, Akld, New Zealand
What sytems or methods are used for cable fault location within different countries and how good is the success rate??

In Auckland NZ in general we use the POPIE ( pool of potential in earth ) for single and multicore non screened cables.

The thumper or HV capacitor discharge is used on Ø to Ø faults or Ø to screen faults in LV and HV cables.

A-frame and signal generator used to pre locate a screen fault on long HV cables and confirmed afterwards with the Popie.

The dart is used for pre analysis of the approx fault distance.
_________________________
The product of rotation, excitation and flux produces electricty.

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#60792 - 01/10/06 04:19 PM Re: Cable Fault location
JoeTestingEngr Offline
Member

Registered: 11/04/05
Posts: 786
Loc: Chicago, Il.
In daylight, we look for the smoke. At night, we look for the flame. When we get close, we sniff for the ozone. But seriously, we have a gizmo with a 600V contactor and a bank of lights. We place it between our DC bus and the load side of an open bridge feeder or traction power breaker. It flashes the lights through the fault. Then we clamp on in various manholes and see the current pulses before the fault, and not after. For signal or control cables I'll give it a shot with a metallic TDR. Guessing the velocity of propagation is always fun but not really that important.
Joe

Top
#60793 - 01/12/06 06:08 AM Re: Cable Fault location
Trumpy Offline


Member

Registered: 07/05/02
Posts: 8553
Loc: SI,New Zealand
The pics that RODALCO submitted can be found here, by clicking right here .
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin

Top
#60794 - 01/12/06 06:26 AM Re: Cable Fault location
mshaw Offline
Member

Registered: 01/11/06
Posts: 45
Loc: Fairborn, Oh, USA
The park that I manage is filled with defence contractors and one day one of them observed me trying to track down a underground fault in my outside lighting. Seems they were testing some equipment that was designed for this purpose to track electrical faults in tanks and aircraft wiring harnesses. They hooked up this small hand held gismo and entered the wire size into the parameters and vada bing it told me which wire had the fault and how many feet it was to the fault from the point that the gizmo was attached, it worked great. I am sure we will be seeing this in civilian applications real soon.

Top
#60795 - 01/12/06 04:20 PM Re: Cable Fault location
JoeTestingEngr Offline
Member

Registered: 11/04/05
Posts: 786
Loc: Chicago, Il.
Mshaw,
The device you mentioned sounds like a TDR. I guess I should have mentioned that TDR stands for Time Domain Reflectometer. They work by sending pulses down conductors or fiber for Optical TDRs. When you get to an impedance change, some energy couples forward, while some reflects back. It works similar to SONAR or RADAR where they gate on a sensitve receiver after the pulse is sent and time the round trip. They calculate the distance to the fault by using the time, speed of light, and the velocity of propagation percentage correction to the speed of light. The guess work I mentioned is because those characteristics vary alot with power conductors and paired cables when compared to coax, and especially fiber. I usually just check a known length of the closest cable I can find and adjust the VP to jive with my sample.
Joe

Top
#60796 - 01/12/06 08:47 PM Re: Cable Fault location
gfretwell Online   content


Member

Registered: 07/20/04
Posts: 9065
Loc: Estero,Fl,usa
We did TDR with a garden variety O scope. You have to do a little math but if you start thinking 2ns a foot and use a little Kentucky windage by causing faults at known locations to get your bearings, you can usually get to the general area of the break/short.
_________________________
Greg Fretwell

Top
#60797 - 01/18/06 04:46 PM Re: Cable Fault location
JoeTestingEngr Offline
Member

Registered: 11/04/05
Posts: 786
Loc: Chicago, Il.
Bump! Boy, that felt good!

Top
#60798 - 01/18/06 07:34 PM Re: Cable Fault location
RODALCO Offline
Member

Registered: 12/08/05
Posts: 865
Loc: Titirangi, Akld, New Zealand
Bump!!

It did

Basic tests prior to fault loaction are:

1. cable safely isolated from supply.
2. both cable ends completely disconnected, including screen earths if used.
3. insulation test Ø to Earth.
4. insulation test Ø to Ø.
5. insulation test screen to earth if applicable.
6. continuity test.

Fault loaction for most screened cables:

7. If possible get the cable route traced with a cable locator if listening devices in conjuntion with a thumper are used.
8. A TDR or Dart can give approximate distance prior to thumping a cable.

For single core non screened cables

9. POPIE, pool of potential in earth can be used very accurately within < 5 cm to pinpoint the fault.
_________________________
The product of rotation, excitation and flux produces electricty.

Top
#60799 - 01/28/06 04:07 AM Re: Cable Fault location
AllClear Offline
Member

Registered: 08/22/05
Posts: 44
Loc: Belmond Iowa US
How Do you use an O-Scope as a TDR? It Sounds like something that could come in handy Someday.
_________________________
It's Not The Fall That Kills You...
It's That Sudden Stop At The End

Top
#60800 - 01/28/06 01:51 PM Re: Cable Fault location
JoeTestingEngr Offline
Member

Registered: 11/04/05
Posts: 786
Loc: Chicago, Il.
How Do you use an O-Scope as a TDR? It Sounds like something that could come in handy Someday.

I didn't say anything at the time but I'm thinking our friend probably had a pulse generator from his laundry room and some kind of gated amplifier from his attic to go with his garden variety O-scope.
Joe

Top
Page 1 of 2 1 2 >


ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals