The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
Yesterday at 09:52 PM
International Wire Colour Codes
by Texas_Ranger
Yesterday at 08:24 AM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 12
renosteinke 6
HotLine1 6
ghost307 5
Potseal 4
Who's Online
1 registered (geoff in UK), 213 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#60759 - 01/09/06 04:16 PM Soda Machines And GFCI's
Wireless Offline

Registered: 06/09/05
Posts: 73
Loc: Los Angeles CA USA
I recently installed a outlet outdoors for a soda machine. I Installed a gfi w/ in use cover. The customer calls today there is not enough power it keeps tripping. So I explain that the gfi won't trip because of too much power. They plugged it in with a extension cord into a regular outlet and it works. What do I do? Take aout the gfi?

Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#60760 - 01/09/06 04:33 PM Re: Soda Machines And GFCI's
Dnkldorf Offline

Registered: 12/12/04
Posts: 1091
Loc: nowhere usa
It could be the GFI is doing it's job, and there is enough leakage current from the compressor to cause the GFI to trip.


#60761 - 01/09/06 04:49 PM Re: Soda Machines And GFCI's
iwire Offline

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
Dnk nailed it.

I would not even think about removing the GFCI.

It's required.

It is probably doing exactly what it is supposed to do.

This is going to be quite an issue until all the vending machines are either fixed or replaced.

I would think we will see an increase in sales of leakage current testers
Bob Badger
Construction & Maintenance Electrician

#60762 - 01/09/06 06:29 PM Re: Soda Machines And GFCI's
frenchelectrican Offline


Registered: 02/06/03
Posts: 938
Loc: Wi/ Paris France { France for ...
the instering issuse with vending machine i did see alot of older unit and i am sure it will be getting pretty messy with new code required gfci on it and yes of course the commpressor do have some current leakage but there are few other source can have current leakage as well.

i know one vending machine did have heat tape inside the soda vending machine and the tape was rotten for some reason and show up with current leakage and replace it.

Merci, Marc
Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)

#60763 - 01/09/06 07:42 PM Re: Soda Machines And GFCI's
Wireless Offline

Registered: 06/09/05
Posts: 73
Loc: Los Angeles CA USA
Thanks for your replies. I remember hearing that you shouldn't put refrigerators on gfi's that is why I asked I wanted to make sure I was right that the gfi had to stay.
Anyway I went out there to take a look when I get there they tell me they fixed it they reset the gfi three times now it works. "Could you just check it" Sure enough the gfi was wet!