The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Son of Sparky
by HotLine1
Yesterday at 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
230 or 345 kV transmission lines?
by annemarie1
10/12/16 01:23 PM
Is this a fix or just a bandaid?
by gfretwell
10/10/16 06:49 PM
New in the Gallery:
12.5A through 0.75mm flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 11
renosteinke 6
HotLine1 6
ghost307 5
Potseal 4
Who's Online
1 registered (Tjia1981), 230 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#6071 - 12/21/01 05:47 PM Lighting contactor
ayrton Offline

Registered: 12/21/01
Posts: 205
Loc: Pa
Question is, I am installing sixty 400w fixtures for parking lot lighting. Add up the wattage and you have 24kw. Now this is a three phase 208/120v system. Since the load is so high I am going to wire for 208v.
In order to size the contactor, when I do my division, do I multiply 1.73 for three phase, which gives me 66 and change or do I leave out the 1.73, because the fixtures are single phase? which would give me 115a.

Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#6072 - 12/21/01 06:42 PM Re: Lighting contactor
electure Offline


Registered: 12/24/00
Posts: 4226
Loc: Fullerton, CA USA
Unless you are installing incandescent fixtures, the load will be more like 460W per fixture (HPS or MH).
Be sure to load the circuit to 80% (or less) of the circuit rating if the load is continuous (more than 3 hrs at a time).

[This message has been edited by electure (edited 12-21-2001).]

#6073 - 12/22/01 03:43 AM Re: Lighting contactor
maintenanceguy Offline

Registered: 12/02/01
Posts: 303
Loc: Southern NJ, USA
I'd like to know the answer to this too. Anyone know?

#6074 - 12/22/01 07:08 AM Re: Lighting contactor
Frank Cinker Offline

Registered: 07/29/01
Posts: 317
Loc: Pennsylvania
When sizing conductors, disconnect switches, contactors etc. I believe the amp value on each ballast must be used, not the wattage of the lamp. For example a 400 watt metal halide fixture operating at 208 V. has a ballast amp value of 2.30 or 478.4 watts per fixture. Multiply 478.4 watts by 60 fixtures = 28,704W / 208V x 1.73 = 79.73 Amps.

A 100 Amp three phase contactor should work fine.

Use 3AWG,THHN Conductor Size.

Assuming the single phase fixtures are balanced properly on the three phase system.

[This message has been edited by Frank Cinker (edited 12-22-2001).]

#6075 - 12/22/01 07:14 AM Re: Lighting contactor
electure Offline


Registered: 12/24/00
Posts: 4226
Loc: Fullerton, CA USA
Yes, if they are supplied by a 3Ø system, you will divide by 1.732
460 / 208 = 2.21A (load per fixture)
2.21A X 60 = 132.6 (total load)
132.6A / 1.732 = 76.6 (load @208v 3Ø)
76.6A X 1.25 = 95.6A (if a continuous load)

Looks like a 100A contactor to me!

#6076 - 12/22/01 09:16 AM Re: Lighting contactor
golf junkie Offline

Registered: 04/22/01
Posts: 511
Loc: York, NE
>Use 3AWG,THHN Conductor Size.

Don't forget voltage drop if applicable.....sometimes those parking lot runs can get pretty long.


#6077 - 12/22/01 09:48 AM Re: Lighting contactor
Bill Addiss Offline

Registered: 10/07/00
Posts: 4196
Loc: NY, USA
To be more correct, We have to say THWN
(assuming underground/wet location installation)

(I call it THHN too)


#6078 - 12/22/01 11:21 AM Re: Lighting contactor
electure Offline


Registered: 12/24/00
Posts: 4226
Loc: Fullerton, CA USA
We must be careful!
I've had my otherwise correct blueprints rejected from plan check 'causa my nasty habit of calling it THHN. They don't buy "You know what I mean".
Here's a couple of things that might help (or maybe not).
Rather than a timed panel, (I'm doing some guessing here), you might consider putting in a large box with listed multi pole lighting contactors rated per your individual branch circuits.
Use a timeclock and photocell to operate this.
A contactor can be used to operate certain security lights that stay on all night via the P/C.
Others can be turned on by P/C, and off by the time clock (just series the P/C and T/C, set the T/C earlier than dark).
You're not limited to 20 amp circuits here if these are HID fixtures, it can be up to a 50A, but you certainly CAN'T use a 100A circuit with #3 wire for anything other than a feeder to smaller C/Bs or fuses.

#6079 - 12/22/01 01:36 PM Re: Lighting contactor
Redsy Offline

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
Can someone explain how a 3 pole contactor will be used to operate these lights? Is a whole panel controlled by a timer a common way to do this?

[This message has been edited by Redsy (edited 12-22-2001).]

#6080 - 12/23/01 06:30 AM Re: Lighting contactor
electure Offline


Registered: 12/24/00
Posts: 4226
Loc: Fullerton, CA USA
The timed panel approach is not that uncommon out here. It's generally used in larger shopping centers where the tenants have their own meters, and the site lighting/signage power is provided by the landlord. With this setup, all the lighting/signage is sure to come on at once.
A smaller panel is usually non-switched, and provides the power for irrigation controls, timeclock power, etc.
I like the setup I mentioned above much better.
(I sure hope that nobody had in mind a single 100A contactor with that circuit run around the parking lot)

[This message has been edited by electure (edited 12-23-2001).]