#60623 - 01/07/06 09:15 AM ark fault
vlad_tepish Offline
Member
Registered: 10/30/05
Posts: 39
Loc: Delavan,Wis,USA
looking for info on ark fault breakers,,,two bedrooms fed with 14-3 ,they share the neut ,when I use my testor everything checks out fine ,put a load on eather room the ark fault breaker trips,,,help???
_________________________
Patrick
Top
Work Gear for Electricians and the Trades
#60624 - 01/07/06 09:31 AM Re: ark fault
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9038
Loc: Estero,Fl,usa
Arc faults also provide GFP protection (30ma GFCI). Some are even GFCI (5ma). In either case you won't be able to share neutral current. This is another reason why we should be able to put the "device" style nearer the point of use than the 2005 code allows. If you could install it in the first outlet after the "split" of the multiwire it would protect the bedroom.
_________________________
Greg Fretwell
Top
#60625 - 01/07/06 10:51 AM Re: ark fault
e57 Offline
Member
Registered: 05/27/03
Posts: 2876
Loc: S.F.,CA USA
Cuttler Hammer makes a good two indivdual circuit AFCI breaker made for 3-wire.

However Vlad it sounds like you have problems circuit or the load. Troubleshooting these can be a real PITA! Contact between another neutral or ground can do that. Most often it would trip right away, but have seen some that remain on until load is applied. Isolate the circuit and check to see if any continuity between the neutral and any other ground or neutral.

Load issues could be anything... Vaccuum cleaner with electronic speed controls, LCD screens, flouresant lighting, dimmers, etc. Many manufacturers have known equipment conflicts that just wont work with the breaker at all.
_________________________
Mark Heller
"Well - I oughta....." -Jackie Gleason
Top
#60626 - 01/07/06 12:46 PM Re: ark fault
HCE727 Offline
Member
Registered: 11/11/05
Posts: 186
Loc: Delaware County, PA, USA
I usually run a 14/2/2 if I am running 2 circuits for afci"s. I would like to check out that breaker, from Cutler Hammer.
_________________________
Hank
Top
#60627 - 01/07/06 01:20 PM Re: ark fault
e57 Offline
Member
Registered: 05/27/03
Posts: 2876
Loc: S.F.,CA USA
http://www.eatonelectrical.com/unsecure/cms1/TB00500002E.PDF

page 27 BR215AF


[This message has been edited by e57 (edited 01-07-2006).]
_________________________
Mark Heller
"Well - I oughta....." -Jackie Gleason
Top
#60628 - 01/07/06 01:30 PM Re: ark fault
togol Offline
Member
Registered: 09/15/05
Posts: 421
Loc: NW In. USA
I thought Wis. deleted the AFCI requirement for 2005? why not just change them out for "normal" breakers
_________________________
Tom
Top
#60629 - 01/16/06 06:52 PM Re: ark fault
vlad_tepish Offline
Member
Registered: 10/30/05
Posts: 39
Loc: Delavan,Wis,USA
replaced the 2 single breakers with a double arkfault ,,everything is fine...thanks
_________________________
Patrick
Top

Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 75 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals