#60618 - 01/06/06 06:16 PM Forklift battery charger
electricman786 Offline
Member
Registered: 09/17/04
Posts: 37
Loc: sacramento
Some one has asked me to hard wire his forklift battery charger. Charger is 3 ph 208/240/480. His panel is providing 208. My question is do we need to open charger to change different input.
Top
Work Gear for Electricians and the Trades
#60619 - 01/06/06 07:30 PM Re: Forklift battery charger
NJwirenut Offline
Member
Registered: 09/15/01
Posts: 806
Loc: Bergen County, NJ
Most likely, yes.

You really need to check the manufacturer's info to be sure.
Top
#60620 - 01/07/06 01:27 AM Re: Forklift battery charger
Larry Fine Offline
Member
Registered: 02/18/05
Posts: 693
Loc: Richmond, VA
I've done a few, and yes, you should open the unit and read the paperwork. They usually come set for a given voltage, but don't assume it's still that way.
_________________________
Larry Fine
Fine Electric Co.
fineelectricco.com
Top
#60621 - 01/07/06 02:53 AM Re: Forklift battery charger
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
Yes open it up, I have never seen one that could adjust itself for different voltages.

You will probably have some jumpers to move and many times you need to change some fuses.

You really got to follow the directions, if you don't have them you can usually get them on line or call the company and they may fax you out a set.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#60622 - 01/07/06 11:08 AM Re: Forklift battery charger
XtheEdgeX Offline
Member
Registered: 04/17/05
Posts: 116
Loc: Florida
Don't forget to check the control transformer as well. I was called to our warehouse to check a charger a co-worker installed. He changed the taps to have it operate on 480, but didn't change the primary on the control transformer. It was still tapped at 208. Needless to say, it didn't like that very much.
Top

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 101 Guests and 13 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Stack, Scotto, Freecrowder, clee512, Jdscott2005

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals