The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
0 registered (), 137 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#6052 - 12/20/01 06:36 PM Connecting Service drop
Joe Carpenter Offline
Member

Registered: 12/19/01
Posts: 55
Loc: USA
What is the preferred method for connecting a triplex overhead feeder to a SE cable at a service entrance head? This is for a 100 amp single phase 120/240 volt subpanel at another building.I know crimp on connectors are often used but if I don't have access to a crimping tool, Can another method be used such as split bolts?
This is somewhat unfamiliar territory for me. I don't know if I even used the proper terminology. My work normally consists of indoor industrial wiring.
I appreciate your help.

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#6053 - 12/20/01 07:03 PM Re: Connecting Service drop
aphares Offline
Member

Registered: 12/17/01
Posts: 39
Loc: Indiana
Split bolt connectors could very well be your next best choice. They are common here.
The only thing to watch for is the UL rating. Split bolt connectors (all-purpose type) are only UL rated for copper and copperweld wires only. but they are advertised for any combination of two dissimilar metals. Most vendors don't know this. One to look for will be dual-rated APS series (NSI), made from tin-plated aluminum. UL (486B) listed for aluminum and copper condutor combinations. The other thing to look out for is a good sealer to avoid moisture, and a very good connection.

Top
#6054 - 12/21/01 02:09 AM Re: Connecting Service drop
Joe Carpenter Offline
Member

Registered: 12/19/01
Posts: 55
Loc: USA
That was my next question. What is the best method of sealing such a connection? And I am assuming that even with a connector that is approved for 2 dissimilar metals, I should still use the anti-oxidizing compound on the connection.

Top
#6055 - 12/21/01 02:33 AM Re: Connecting Service drop
sparky Offline
Member

Registered: 10/18/00
Posts: 5545
Joe,
my personal method is to make the connection using no-lox, seal it with scotchcoat, apply a thin layer of dux seal, then wrap with splicing tape. The theory being to seal it from atmosphere.

Top
#6056 - 12/21/01 04:18 AM Re: Connecting Service drop
electure Offline

Member

Registered: 12/24/00
Posts: 4226
Loc: Fullerton, CA USA
You might check with your supplier. Many wholesalers have a Hypress crimper that they'll rent/loan to you.
I make the split bolt connections much as Sparky stated.
Make connection with NoAlox (using connectors properly rated with separators for the Cu/Al connection). Wrap the connection with #130 linerless rubber tape. Then put on Scochkote, and finally tape with regular elect tape. It keeps the gook off of the split bolt if you want to access it later.
If there is a possibility of abrasion, use varnished Cambric tape over the Scotchkote, and under the elect tape.

Top
#6057 - 12/23/01 09:26 AM Re: Connecting Service drop
golf junkie Offline
Member

Registered: 04/22/01
Posts: 511
Loc: York, NE
I think that I could make a full time living repairing loose split bolt connections on overhead wiring.

If there is anyway possible....use crimps. The combination of wind and aluminum wiring is just the recipe for a loose connection some years in the future.

GJ

Top
#6058 - 12/25/01 08:39 AM Re: Connecting Service drop
silverbk Offline
Member

Registered: 02/24/01
Posts: 61
Here in NY The power companies won't allow split bolts anymore. I have repaired many, in years past. As soon as a customer says half my house is out that's where I look.

We now have to use either Hypress type connectors, most supply houses will rent you a mechanical crimper.

Or paralell groove connectors. Con Edison is only allowing a specific type of connector made by Richards, they come pre noaloxed and come with a plastic snap on cover.

Top
#6059 - 12/28/01 02:03 PM Re: Connecting Service drop
The Watt Doctor Offline
Member

Registered: 12/23/01
Posts: 443
Loc: Mont Belvieu, TX
Copper/Aluminum split bolt (for copper to aluminum connections), scotch 33 wrapped on backwards (sticky side out), cambric, linerless rubber (or scotch pad), scotch 33 again (sticky side down this time), and a layer of friction tape is my formula for noncrimp connections.
I use the same for gutters when I have to use split bolts. The backwards tape is used to make it easy on someone if they ever have to break those connections.
HMEL#688
_________________________
The Watt Doctor
Altura Cogen
Channelview, TX

Top
#6060 - 12/29/01 07:46 PM Re: Connecting Service drop
Jim M Offline
Member

Registered: 08/10/01
Posts: 453
Loc: Chestertown, MD, USA
Although the utility here cuts i their own drops with crimps, I have found the pre-insulated taps from NSI or Polaris to be a real time and labor saver on service upgrades when making a temporary connection to provide power until the inspection and final cutover. Be sure to get them back as they are almost $30 each for a 4/0 size.

Top
#6061 - 12/30/01 10:01 PM Re: Connecting Service drop
spkjpr Offline
Member

Registered: 12/01/00
Posts: 226
Loc: Sedalia,MO, USA
Hey Watt Dr glad to see someone else tapes a splice with 33 before using splice tape. It does make it easier to undo later. I work on several pump motors we have to replace on a semi- regular basis that have the connections covered in splice tape and one guy does not use 33 before the splice tape, sure hate following him. Usually takes a day for the bleeding to stop after cutting the splice tape off.