#59814 - 12/15/05 05:10 AM Lights flicker
sandro2 Offline
Member
Registered: 03/26/05
Posts: 49
Loc: philadelphia,PA
I received a call of lights flickering at a restaurant when the dishwasher kicks on.
What are some things to look for.
I checked for loose neutrals,hots.
They are on different circuits
Top
Work Gear for Electricians and the Trades
#59815 - 12/15/05 05:34 AM Re: Lights flicker
pauluk Offline
Member
Registered: 08/11/01
Posts: 7520
Loc: Norfolk, England
Flickering as in actually going on and off a time or two, or just a momentary dip in brightness?

If the latter then it might just be the normal momentary voltage drop on the feeder caused by the switch-on surge of the motor.
Top
#59816 - 12/15/05 05:46 AM Re: Lights flicker
sandro2 Offline
Member
Registered: 03/26/05
Posts: 49
Loc: philadelphia,PA
a momentary dip in brightness.
Top
#59817 - 12/15/05 05:47 AM Re: Lights flicker
sandro2 Offline
Member
Registered: 03/26/05
Posts: 49
Loc: philadelphia,PA
Is there any way to solve this. It looks really bad when you have many people in a restautant and the lites dim every so often.
Top
#59818 - 12/15/05 06:19 AM Re: Lights flicker
Dnkldorf Offline
Member
Registered: 12/12/04
Posts: 1064
Loc: nowhere usa
What type of lights, incandesant or fluro?

Dnk...
Top
#59819 - 12/15/05 06:37 AM Re: Lights flicker
sandro2 Offline
Member
Registered: 03/26/05
Posts: 49
Loc: philadelphia,PA
incadescent
Top
#59820 - 12/15/05 09:01 AM Re: Lights flicker
earlydean Offline
Member
Registered: 12/22/03
Posts: 751
Loc: Griswold, CT, USA
Aside from moving the lights from phase A to phase B, or upgrading the service so that the dishwasher load won't appreciably effect the available voltage to the lights, or reducing the load to the lighting circuit by sharing the circuits, I guess the only thing is to reduce the draw on the dishwasher. Can the dishwasher be connected 240 volts? How about 3 phase?
_________________________
Earl
Top
#59821 - 12/15/05 09:09 AM Re: Lights flicker
sandro2 Offline
Member
Registered: 03/26/05
Posts: 49
Loc: philadelphia,PA
The service is new. I guess I can try and see if the manufacture has a 240v model instead
Top
#59822 - 12/15/05 06:36 PM Re: Lights flicker
ShockMe77 Offline
Member
Registered: 06/11/05
Posts: 821
Loc: Rahway, New Jersey
I would check and see if both circuits were on the same phase. If they are on the same phase, put one of the two on a different phase. It's worked for me before. Good luck!
Top
#59823 - 12/15/05 08:00 PM Re: Lights flicker
sierra electrician Offline
Member
Registered: 02/12/05
Posts: 219
Loc: North Fork, CA USA
If the PoCo Xfmr is shared, the loads at the neighbors house can cause the lights to flicker and dim. I the dwelling is at or near the end of the Poco ckt this can happen too. This may not be the problem but, you could be chasing ghosts.

Rob
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (gfretwell), 54 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals