I'm installing a 1.5 hp 230V 11 amp single phase fan motor from a 120/208V panel about 250 feet away. Any suggestions for wire size.
Top
Work Gear for Electricians and the Trades
#59697 - 12/12/05 07:37 PM Re: suggested wire size
bot540 Offline
Member
Registered: 09/14/04
Posts: 174
Loc: Vernon Hills, IL
YOU'LL NEED TO PULL NO. 8 WIRE
_________________________
Jesus may have been a capenter,but God was an electrician.Genesis1:3
Top
#59698 - 12/12/05 08:08 PM Re: suggested wire size
George Offline
Member
Registered: 02/23/02
Posts: 375
maybe only #10.
Top
#59699 - 12/12/05 08:31 PM Re: suggested wire size
Bob Offline
Member
Registered: 02/05/02
Posts: 182
Loc: Mobile, AL, USA
JK
Have you tried to do the VD caculations yourself?
Top
#59700 - 12/12/05 09:50 PM Re: suggested wire size
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
10 drops 6.6v, 12 drops 10.6v @ 11a
_________________________
Greg Fretwell
Top
#59701 - 12/13/05 02:53 AM Re: suggested wire size
jkraft Offline
Member
Registered: 05/05/03
Posts: 74
Bob,

I apologize, I have not. I was hoping someone would have previous experience with this.

Joe
Top
#59702 - 12/13/05 04:02 AM Re: suggested wire size
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
Not all 230 volt rated motors are suitable for use on 208 volt systems. The voltage drop will make this problem worse.
Don

[This message has been edited by resqcapt19 (edited 12-13-2005).]
_________________________
Don(resqcapt19)
Top
#59703 - 12/13/05 06:17 PM Re: suggested wire size
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5316
Loc: Blue Collar Country
Don is quite right; even under the best of conditions, you're really pushing it when you try to run a "230v" motor on 208 volts.

As a general rule of thumb, a motor may be used at plus or minus 10% of the nameplate marked voltage. So if your nameplate avtually reads simply "230v", then it should have a minimum of 207 volts at all times- and make sure that value is measured "under load!"

Now, if the motor is marked 220, or 208/230, etc...well, you get the picture.

I would also be very conservative in allowing for voltage drop. Remember, motors- especially those used in compressors- have a considerably higher curent required for starting; you almost want to base your voltage-drop calculations on the "LRA", or 'locked rotor amps.'

An exhaust fan isn't really fighting a load as it is starting up; so the inrush current needed isn't as great as it might be in other applications. You will probably be able to use #8.

One thing to also consider is a motor satrter with electronic overloads ("heaters"). Even though strictly not necessary, it will provide additional protection for the motor. The electronic elements provide protection against many other power problems than simple 'heaters' do.
Top

Member Spotlight
Member Since: 01/22/05
Posts: 5316
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 95 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals