#59656 - 12/12/05 04:42 PM 3 wire for new construction?
NJ Wireman Offline
Member
Registered: 08/26/04
Posts: 179
Loc: New Jersey (South Jersey)
I was told that for the new 2005 code that (NM) romex for applainaces ie; water heater, ac disconnect, dryer must now be in 3 wire. Is this true and if so can some one please state a code # reference. I am racking my head trying to find this but have been unable.
Top
Work Gear for Electricians and the Trades
#59657 - 12/12/05 04:50 PM Re: 3 wire for new construction?
Roger Offline
Member
Registered: 05/18/02
Posts: 1779
Loc: N.C.
There is no such NEC requirement, a 2 conductor with ground is all that is needed

Roger
Top
#59658 - 12/12/05 04:52 PM Re: 3 wire for new construction?
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
You can not feed a 240/120 dryer with a 3 wire.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#59659 - 12/12/05 05:01 PM Re: 3 wire for new construction?
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country
One must ask the question right, to get the answer right :-)

At one time- not so long ago- it was the practice to "ground" the case of a range or clothes dryer by bonding it to the third wire- which also served as the "neutral" for any 110 loads the appliance might have had.

This is no longer allowed on NEW dryers and ranges, nor is it allowed to run NEW circuits this way. Section 250.140 is the place to start reading...

So, today, we no longer bond the case to the "neutral" wire. We run an additional wire to serve as the ground wire.

If an appliance has no 110v loads, then the third prong of the plug is a true "ground" prong.
Top
#59660 - 12/12/05 05:12 PM Re: 3 wire for new construction?
NJ Wireman Offline
Member
Registered: 08/26/04
Posts: 179
Loc: New Jersey (South Jersey)
so renosteinke
then would you or wouldn't you use 3 wire?

i have done several ovens micro/convection over the last year where they came with a set up of a black , a red, a neutral and a ground? for a 220 set up 30 amp and man i must say i love this place that was quick 3 responces in no time. Gotta love it thanks kenny
Top
#59661 - 12/12/05 05:20 PM Re: 3 wire for new construction?
Roger Offline
Member
Registered: 05/18/02
Posts: 1779
Loc: N.C.
Whoa, I only (stopped reading at) read "water heater and ac disconnect", shame on me.

Iwire and John are correct, on 120/240v appliances, a three insulated conductor with equipment grounding conductor wiring method must be used.


Roger
Top
#59662 - 12/12/05 05:36 PM Re: 3 wire for new construction?
NJ Wireman Offline
Member
Registered: 08/26/04
Posts: 179
Loc: New Jersey (South Jersey)
but john says yes and i wire says no?
Top
#59663 - 12/12/05 06:05 PM Re: 3 wire for new construction?
Electricmanscott Offline
Member
Registered: 01/12/02
Posts: 1478
Loc: Holden, MA USA
Two hots, one neutral and one ground (very untechnical I know) require two hots, one neutral and one ground feeding it.
Top
#59664 - 12/12/05 06:08 PM Re: 3 wire for new construction?
Roger Offline
Member
Registered: 05/18/02
Posts: 1779
Loc: N.C.
NJ Wireman, actually I think John and Iwire are saying the same thing,

Iwire said
Quote:
You can not feed a 240/120 dryer with a 3 wire.


I think Iwire means there must be four conductors

John said
Quote:
So, today, we no longer bond the case to the "neutral" wire. We run an additional wire to serve as the ground wire.


Roger



[This message has been edited by Roger (edited 12-12-2005).]
Top
#59665 - 12/12/05 06:58 PM Re: 3 wire for new construction?
NJ Wireman Offline
Member
Registered: 08/26/04
Posts: 179
Loc: New Jersey (South Jersey)
I see i thought when he said three wire, i mis understood. I thank all for their help.
Top
Page 1 of 2 1 2 >

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Forum Styles
by Admin
Today at 02:22 PM
License exam
by TRUE POWER
Yesterday at 09:16 PM
Looking for older post
by sparkyinak
Yesterday at 12:27 AM
Members: Non-Members: Did you know?
by Admin
01/22/17 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM

Who's Online
1 registered (Admin), 105 Guests and 18 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Member Since: 08/17/06
Posts: 358

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals