#59619 - 12/09/05 05:23 PM Street Lighting
distributor x Offline
Member
Registered: 07/28/05
Posts: 57
Loc: Canada
I was driving home last night, and the HPS streetlighting all along the freeway was strobing, flashing on and off approx once per second.

I did not think it was possible for HPS to have such a quick restrike time

What could have caused this?
Top
Work Gear for Electricians and the Trades
#59620 - 12/10/05 01:45 AM Re: Street Lighting
e57 Offline
Member
Registered: 05/27/03
Posts: 2876
Loc: S.F.,CA USA
The Lucalox Superlife have no re-strike time, there are some other lamps made like this as well.
http://www.gepc.pl/lighting/do_pobrania/Lucalox%20-%20Ulotka%20(angielski).pdf

Also, on page 4 they have a short explaination of why they might be blink off and on, possibly due to wind or traffic vibration? Next guess would be strange voltage disturbance?
_________________________
Mark Heller
"Well - I oughta....." -Jackie Gleason
Top
#59621 - 12/10/05 05:06 AM Re: Street Lighting
earlydean Offline
Member
Registered: 12/22/03
Posts: 751
Loc: Griswold, CT, USA
I once went to a seminar put on by a lighting manufacturer. The only thing that I remember about the context is the fact that if a HPS fixture cycles on and off, it is the bulb. Through the years, I have followed this rule, and have found it to always be true.
_________________________
Earl
Top
#59622 - 12/10/05 05:54 AM Re: Street Lighting
jwhite Offline
Member
Registered: 12/01/05
Posts: 64
Loc: Trenton, NC, USA
the restrike time is proportioinal to how hot the bulb is. if the bulb is not hot because it didnt light completely before the next power interuption it will restrike faster.
Top
#59623 - 12/10/05 10:37 AM Re: Street Lighting
mxslick Offline
Member
Registered: 10/24/04
Posts: 803
Loc: Atomic City, ID USA
Some years back a shopping center had the same thing happening to an entire parking lot. They later found the cause when the circuit breaker caught fire. (It was arcing internally until it finally failed.)

So I would think that anything which causes an arc fault on the circuit would cause that effect. (Bad underground splice/feeder, etc.)

Arc faults would chop the current so fast that the bulb wouldn't go completely out, so it can strobe faster than the igniter would pulse it.

Were you a good samaritan and called the highway dept.?
_________________________
Stupid should be painful.
Top

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (HotLine1), 111 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals