#59553 - 12/07/05 12:48 PM Generator Disconnect
SJT Offline
Member
Registered: 07/24/02
Posts: 241
Loc: PATCHOGUE, N.Y.
Is a disconnect required to be installed next to a transfer switch (industrial, campus type setting) for the generator feeder. There is a generator remotely installed away from a Bldg. and the generator power enters a mechanical room. Normally, I've seen the gen. feeder go right to the transfer switch. I think it's good design, in case you want to isolate Generator power for a test, and or trouble shooting job.
Is there anything in the code that requires such a disconnect? Thanks
Top
Work Gear for Electricians and the Trades
#59554 - 12/07/05 01:33 PM Re: Generator Disconnect
jwhite Offline
Member
Registered: 12/01/05
Posts: 64
Loc: Trenton, NC, USA
445.18 Disconnecting Means Required for Generators.
Generators shall be equipped with disconnect(s) by means
of which the generator and all protective devices and control
apparatus are able to be disconnected entirely from
circuits supplied by the generator except where both of
following conditions apply:
(1) The driving means for the generator can be readily
down.
(2) The generator is not arranged to operate in parallel
another generator or other source of voltage.
Top
#59555 - 12/07/05 06:39 PM Re: Generator Disconnect
Electric Eagle Offline
Member
Registered: 04/20/02
Posts: 914
Loc: Alpharetta, GA
Most/All generators have a main breaker in the generator, this serves as the disconnecting means for the feeder to the transfer switch.
Top

Member Spotlight
Member Since: 10/07/00
Posts: 3417
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 54 Guests and 6 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals