#59536 - 12/06/05 06:36 PM Fire damage
livetoride Offline
Member
Registered: 01/11/05
Posts: 109
Loc: san diego ca usa
I went on a call today where there was an arson fire on one side of the medical mini mall. The fire department had killed the main. My job was to get as much power back as was safe. I checked the damaged suite and it happened to be the last one furthest away from the main service. I turned off all the breakers in the MDP and looked inside the cabinet for any damage. I then turned on the main. Then after checking for damage went to each sub panel turned off all the breakers and checked then turned each panel one at a time. Aside from the totaled suite there were 4 cks that tripped. Any ideas that would improve what I did? I am not worried about the tripping breakers now just needed power and lights for clean up. Rod
Top
Work Gear for Electricians and the Trades
#59537 - 12/06/05 08:24 PM Re: Fire damage
e57 Offline
Member
Registered: 05/27/03
Posts: 2876
Loc: S.F.,CA USA
Check for water and heat damage, then, after testing for shorts first, go turn things back on. It would be bad to have the fire dept out again, after a short did not clear, or someone got zapped.
_________________________
Mark Heller
"Well - I oughta....." -Jackie Gleason
Top
#59538 - 12/06/05 09:42 PM Re: Fire damage
JoeTestingEngr Offline
Member
Registered: 11/04/05
Posts: 781
Loc: Chicago, Il.
I suppose you could have used a Megger if you have one. Just don't go gung ho on voltage setting and watching for sensitive loads. Meter down the line of breakers to neutral before closing in on anything that is obvioulsly faulted.
Joe
Top
#59539 - 12/06/05 10:24 PM Re: Fire damage
livetoride Offline
Member
Registered: 01/11/05
Posts: 109
Loc: san diego ca usa
<Check for water and heat damage>
Did that as I went from suite to suite both before and after turning on the circuits.

No megger on the truck. I did take ohms and amp readings.Also the faults I did have were from the FD breaking conduit and flex. Rod
Top

Member Spotlight
Member Since: 08/22/05
Posts: 44
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 45 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals