#5953 - 12/16/01 12:40 AM Beeping GFCI?  
sparky66wv  Offline
Member
Joined: Nov 2000
Posts: 2,232
West Virginia
Got a troubleshooting call today:

"My Ground Fault Outlet started beeping, then it tripped after a little puff of smoke came out..."

Beeping?!?!?!

A standard Leviton 6599I 15A 125V with 20A feedthru... Not even the new LED trip indicator light...

Beeping?!?!?!?

I dissected the Receptacle after the report of smoke, to find no heat damage but...

I found some cobwebs and two "meal worm" carcasses... one crispy fried...

Do "meal worms" beep before they die?

Beeping?!?!?!

[Linked Image]


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI

Work Gear for Electricians and the Trades

#5954 - 12/16/01 01:06 AM Re: Beeping GFCI?  
ElectricAL  Offline
Member
Joined: Oct 2001
Posts: 597
Minneapolis, MN USA
'66

Ya got me!!

But that's the best laugh I've had today! [Linked Image]

Al


Al Hildenbrand

#5955 - 12/16/01 04:03 AM Re: Beeping GFCI?  
njelectricmaster  Offline
Member
Joined: Apr 2001
Posts: 109
Lead, South Dakota
Hello from Colorado!!!!!!

You know that all electrical devices have a certain amount of smoke built into them, and when all the smoke escapes it is time to replace it!!!!! ha,ha,ha!!!


Jon Niemeyer

#5956 - 12/16/01 04:06 AM Re: Beeping GFCI?  
njelectricmaster  Offline
Member
Joined: Apr 2001
Posts: 109
Lead, South Dakota
Hello from Colorado!!!!!!

You know that all electrical devices have a certain amount of smoke built into them, and when all the smoke escapes it is time to replace it!!!!! ha,ha,ha!!!

'66, my wife says that if you have meal worms in your flour and accidentally throw them in a hot pan, they make a small screeching sound as they fry!!

:-) JON


Jon Niemeyer

#5957 - 12/16/01 08:30 AM Re: Beeping GFCI?  
pauluk  Offline
Member
Joined: Aug 2001
Posts: 7,520
Norfolk, England
Maybe your customer was trying to describe an arcing sound, or even the buzzing of a magnetic trip on the verge of operating??? [Linked Image]

Yeah, I know we'd never think that either of those sounds could remotely be described as "beeping," but I've found plenty of people who use descriptive words like that in bizarre ways!


#5958 - 12/16/01 08:42 AM Re: Beeping GFCI?  
electure  Offline


Member
Joined: Dec 2000
Posts: 4,259
Fullerton, CA USA
Yes!! I have some mealworms left from fishing, just threw a couple in a hot pan.
More like the squeak a lobster makes when thrown in boiling water. Got to go clean it up before my wife catches me


#5959 - 12/16/01 12:40 PM Re: Beeping GFCI?  
Cindy  Offline
Member
Joined: Jun 2001
Posts: 196
PDX, OR, US
electure, you're mean [Linked Image]
would your local SPCA have something to say about this?

[This message has been edited by Cindy (edited 12-16-2001).]


#5960 - 12/16/01 01:53 PM Re: Beeping GFCI?  
motor-T  Offline
Member
Joined: Nov 2001
Posts: 280
Girard, Ohio, USA
Cindy
Actually it no worse than drowning worms for fishing. Heck I catch flies all the time for fishing, they just dont wanna stay on the hook.


#5961 - 12/16/01 02:39 PM Re: Beeping GFCI?  
sparky66wv  Offline
Member
Joined: Nov 2000
Posts: 2,232
West Virginia
Thanks for the replies and experiments!

At least I'm not going crazy...


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI

#5962 - 12/16/01 05:31 PM Re: Beeping GFCI?  
Bill Addiss  Offline
Member
Joined: Oct 2000
Posts: 3,875
NY, USA
electure,

You going Ice Fishing out there? [Linked Image] It's starting to get pretty cool around here lately.

A local radio station played an April fools day prank last year I think, where they told everyone to unplug their Telephones and cover the Jacks because the Telco was going to be cleaning out their lines and you didn't want the dust coming out. They had people calling in from cell phones asking things like "is the bird going to be OK in that room?" Good Stuff !! [Linked Image]

Bill


Page 1 of 2 1 2

Member Spotlight
HCE727
HCE727
Delaware County, PA, USA
Posts: 186
Joined: November 2005
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.024s Queries: 15 (0.003s) Memory: 0.8155 MB (Peak: 0.9898 MB) Zlib enabled. Server Time: 2017-03-23 00:16:49 UTC