The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
International Wire Colour Codes
by Tjia1981
Today at 12:08 PM
Parking lot pole light swap....
by HotLine1
Today at 09:39 AM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 12
HotLine1 7
renosteinke 6
ghost307 5
Potseal 4
Who's Online
0 registered (), 244 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#59150 - 11/28/05 05:59 PM 30 amps through 14 awg wire !
rowd Offline

Registered: 09/13/02
Posts: 31
Loc: Park Forest, Illinois, USA
I was talking to my mortgage broker today and he said:
"Why does my wiring hum?"
I asked min to describe what he had plugged in. He said:

"I was plugging in Christmas light and kept blowing the breaker so i got into the panel and changed the breaker. But when the xmas light are on you can hear a low pitched hum."

I said:

"What size breaker did you replace the old breaker with and he said 30 amp"

I almost fainted............

I explained to him how dangerous this was and to immidiatly take out the 30amp breaker and put the 15amp back in.

Now I've long suspected that if you exceed the amperage rating of a conductor it vibrates but have never tested this. Anyone care to confirm this?

Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#59151 - 11/28/05 06:45 PM Re: 30 amps through 14 awg wire !
PCBelarge Offline

Registered: 06/08/03
Posts: 657
Loc: Dobbs Ferry, NY, USA

You may have been mistaken. This time of year, there are many Xmas songs.... and remembering the words to all of them is difficult. I believe the wires were humming, as they did not know the words

Sorry... Actually I believe what you posted is pretty good.
Pierre Belarge

#59152 - 11/28/05 06:59 PM Re: 30 amps through 14 awg wire !
ShockMe77 Offline

Registered: 06/11/05
Posts: 823
Loc: Rahway, New Jersey
I come across this alot, especially in the inner city. Seems that people who cannot afford an electrician just fix the problem themselves by going to a larger breaker/ twist-in fuse. It's a shame because this is one of the easiest ways to start an electrical fire. Like the saying goes, good electricians aren't expensive, they're priceless!

#59153 - 11/28/05 07:10 PM Re: 30 amps through 14 awg wire !
winnie Offline

Registered: 09/15/03
Posts: 652
Loc: boston, ma
I don't think that this pertains to overload specifically, but simply something that happens whenever current flows; conductors move when current flows through them. Conductors in a circuit tend to push themselves apart. The force will be roughly proportional to the square of the current flow, so the effects of this force will be more noticeable the higher current is. I've seen large cables jump during short circuit conditions.


#59154 - 11/28/05 07:45 PM Re: 30 amps through 14 awg wire !
lamplighter Offline

Registered: 10/05/05
Posts: 101
Loc: Clawson,Michigan,USA
I agree, I once had the priveledge to wire a testing station for spot welding guns for automotive manufacturing.
The leads to the guns were about eight feet long and made of 500mcm welding cable.
the cables would just hang there, side by side, until you threw the juice to them and then they would jump straight up and over so that they were 180 degrees apart and as far away from eachother as possible.
It was fun to watch.

#59155 - 11/28/05 07:54 PM Re: 30 amps through 14 awg wire !
BigB Offline

Registered: 03/31/04
Posts: 725
Loc: Tucson, AZ USA
I have a good sized air compressor which runs on 120 or 240. I am currently running it on 120. It is plugged into a receptacle which is wired with thhn in emt. Every time it starts I can hear what sounds like one or two of the thhns slapping against the inside of the emt, very distinctly. I think the thhns are solid. I have also heard thhns inside emt make a lot of buzzing when energizing into a short circuit.

#59156 - 11/28/05 08:09 PM Re: 30 amps through 14 awg wire !
LK Offline


Registered: 01/21/03
Posts: 1721
Loc: New Jersey
We get to home on a service call, wife called with bedroom circuit will trip breaker, so we look in the bedroom, TV, Computer with printer, electric baseboard space heater, at this point she informs us that her husband has fixed this type of problem before, so we go to the basement, and look at the panel, every 15 and 20 amp breaker except the bedroom circuit, was replaced with 30Amp breaker, we advised her this was a dangerous condition, and explained proper circuit protection, at this point, she went to the phone, and called her electrical expert husband, she returned from the phone, to tell us to please leave my house, my husband said, he will call someone that knows what they are doing.

#59157 - 11/29/05 03:37 AM Re: 30 amps through 14 awg wire !
Steve Miller Offline

Registered: 08/30/01
Posts: 322
Loc: Loudoun Cty, VA
Yes they will hum, usually not for long. Then they'll burn. Another example of this that is legal and normal is a large diesel geny (250-500 or so) as it starts. Watch the battery cables. The huge draw that occurs when the diesel starts causes the cables to shake and hum/scream for just an instant.

#59158 - 11/29/05 06:05 AM Re: 30 amps through 14 awg wire !
Mike Wescoatt Offline

Registered: 06/17/01
Posts: 164
Loc: Cedar City, Utah
LK, did you hand her the phone number for the local fire station?

If you make something idiot proof, someone will invent a better idiot.

Really, for their sake, I hope they called another electrician. They might see a pattern emerging in the advice they're given.
Mike Wescoatt

#59159 - 11/29/05 07:04 AM Re: 30 amps through 14 awg wire !
mamills Offline

Registered: 11/30/01
Posts: 739
Loc: Wharton, Texas, USA
LK: I wonder what qualifies her husband as an "electrical expert"? It's obviously not the same standard that qualifies real electricians.

All too often, I have seen overfusing and "overbreakering" reduced to merely a matter of economics and convenience. The 15 amp fuse blows (or breaker trips), so I will put in a 30. It costs the same and you don't have that annoying blowing.

Logic without reason... . It keeps the Fire Departments and the Funeral Homes operating.

Mike (mamills)