#59050 - 11/25/05 12:04 AM Do Not Break Sign on Breaker!!
Wireless Offline
Member
Registered: 06/09/05
Posts: 73
Loc: Los Angeles CA USA
I was at a job today and noticed on some the breakers a metal bracket with a set screw in it over the switch on the breaker so that no one would shut that breaker off. They even took off the common tie on the main to put these brackets on is the breaker still able to trip?
Top
Work Gear for Electricians and the Trades
#59051 - 11/25/05 02:55 AM Re: Do Not Break Sign on Breaker!!
George Corron Offline
Member
Registered: 05/16/01
Posts: 717
Loc: Lorton, Va USA
Locking a breaker in the energized position does not affect it's ability to open the circuit. Very common (and legal, BTW) practice for mission critical and some life safety equipment.
Top
#59052 - 11/25/05 04:48 AM Re: Do Not Break Sign on Breaker!!
LearJet9 Offline
Member
Registered: 04/24/05
Posts: 197
Loc: Millis, MA USA
You indicate "they took off the common tie." If this is a multi-pole breaker taking off the common tie does in fact violate NEC rules. That means that 1 of the poles can trip leaving the other pole(s) live. No a good situation.
Top
#59053 - 11/28/05 08:26 AM Re: Do Not Break Sign on Breaker!!
dlhoule Offline
Member
Registered: 04/28/05
Posts: 73
Loc: Saline, MI 48197
We have a lot of energy conscious people here where I work. Prior to installing these clips on single pole breakers feeding emergency lighting and exit signs. We would frequently fail our monthly inspections due to batteries having been discharged without adequate time to recharge.

They are legal and at times provide a simple solution to a problem.
Top
#59054 - 11/28/05 01:11 PM Re: Do Not Break Sign on Breaker!!
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
Lear

Quote:
You indicate "they took off the common tie." If this is a multi-pole breaker taking off the common tie does in fact violate NEC rules. That means that 1 of the poles can trip leaving the other pole(s) live. No a good situation.


While I agree taking the factory installed handle is a violation I do not agree with the rest of your statement.

A "Common Trip Breaker" will trip all poles on a short or overload regardless of the handles. A "Common trip Breaker" has an internal mechanism to make sure of that.

The only thing that handle ties ever guarantee is the opening or closing of all poles when switched by hand.

Bob
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 93 Guests and 11 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals