Hello everyone
Posted SEU meant SER
I have a few questions regarding service entrance cable.
Is it possible to come from the meter can through the wall and up without violating the bend radius. The walls are framed with 2 x 4’s.
The actual diameter of the conductors in 4/0 aluminum SE cable appears to be aprox. 5/8 to 3/4 an inch. 3/4 x 5 = 3 and 3/4 inch bending radius.
Also this puts the cable very close to the finished surface. Wouldn’t this require nail plates?
I have seen this done many times and always passed inspection. I am interested in doing things proper, not just passing inspection.



[This message has been edited by kdal (edited 11-22-2005).]
Top
Work Gear for Electricians and the Trades
#58831 - 11/22/05 09:13 AM Re: seu bend radius
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
The only place the code requires the 1.25" setback is next to framing members.
I don't like it, or even agree but that is the way it reads and the way it gets enforced here.
A agree with your concern on service entrance conductors. I would probably go after that with 250.30(A)(1)
<service disconnect shall be>... "nearest the point of entrance of the service conductors." and tell them the "up" has to happen outside the building with the penetration right behind the service disconnect.
_________________________
Greg Fretwell
Top
#58832 - 11/22/05 09:22 AM Re: seu bend radius
macmikeman Offline
Member
Registered: 07/16/02
Posts: 717
Loc: Honolulu, Hawaii
We have a couple of inspectors that won't allow that method on 2x4 construction walls for anything bigger than #2 ser. The minimum bending radius for Ser cable is based on the outside dimensions of the cable, not the conductors. With 4/0 cable you won't be able to make a small enough bend to meet code and stay inside the wall at the same time. See 338.24.
Top

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 93 Guests and 11 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals