#58779 - 11/19/05 02:51 AM ground rods
huungrycat Offline
Junior Member
Registered: 04/04/02
Posts: 7
Loc: myrtle beach,s.c.usa
if i run a 2/0 ground wire to the ground rod,how many ground rods do i install.do grnd rods have a specific size?mfg cannot answer this.i shouldnt have to run reststance tests untill i get enouge rods in. been too long. i used to know this.im getting too old i guess.rw
Top
Work Gear for Electricians and the Trades
#58780 - 11/19/05 03:23 AM Re: ground rods
Roger Offline
Member
Registered: 05/18/02
Posts: 1716
Loc: N.C.
Per the NEC, the rod must be a minimum of 5/8" in diameter, {250.52(A)(5)(b)}you would never need more than two rods and a #6 for the GEC.

If you are trying to meet a performance spec, you would need to install as many as it takes to get to the resistance number set by the spec and a larger conductor would help.

Roger

[This message has been edited by Roger (edited 11-19-2005).]
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
2 registered (ampherder, sparkyinak), 56 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
KrmtFrg, Stack, Scotto, Freecrowder, clee512

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals