The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
Today at 03:17 PM
Calling all Non-US members!! (Non-US only)
by aussie240
Yesterday at 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
sparkyinak 8
Texas_Ranger 8
Trumpy 6
Who's Online
0 registered (), 256 Guests and 6 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#58769 - 11/18/05 09:10 PM No Main Disconnect on Panel?
aldav53 Offline
Member

Registered: 08/22/01
Posts: 547
Loc: Chandler, AZ USA
Saw a residential breaker panel today that was an old Murrey split buss panel. It did not have a main disconnect. It was fed underground to the meter and directly from the meter with 3/0 wire and thats it. Are these fused at the transformer?
_________________________
The Golden Rule - "The man with the gold makes the rule"

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#58770 - 11/18/05 09:30 PM Re: No Main Disconnect on Panel?
Trumpy Offline

Member

Registered: 07/05/02
Posts: 8540
Loc: SI,New Zealand
Al,
That sounds like a nightmare!.
How can you have a panel without any disconnect switch in it?
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin

Top
#58771 - 11/18/05 09:38 PM Re: No Main Disconnect on Panel?
aldav53 Offline
Member

Registered: 08/22/01
Posts: 547
Loc: Chandler, AZ USA
I don't know, but there definetly was not a main disconnect. I can't ever remember seeing this. I'll check to see if the whole neighborhood was this way. I'm guessing it was.
_________________________
The Golden Rule - "The man with the gold makes the rule"

Top
#58772 - 11/18/05 09:51 PM Re: No Main Disconnect on Panel?
stamcon Offline
Member

Registered: 03/24/01
Posts: 322
Loc: So San Francisco CA
If it was a split bus panel, were there 6 breaker positions on the line side of the buses?

steve

Top
#58773 - 11/19/05 02:46 AM Re: No Main Disconnect on Panel?
huungrycat Offline
Junior Member

Registered: 04/04/02
Posts: 7
Loc: myrtle beach,s.c.usa
YOU INSTALL A BREAKER IN THE TOP SECTION TO FEED THE LOWER SECTION THIS KEEPS YOU WITHEN THE 6 RULE

Top
#58774 - 11/19/05 05:10 AM Re: No Main Disconnect on Panel?
winnie Offline
Member

Registered: 09/15/03
Posts: 652
Loc: boston, ma
230.71 permits a set of up to six breakers or switches to be used as the 'service disconnecting means'. The split buss panels would have 6 breakers feeding things like the electric range, dryer, AC, etc. with one of these breakers feeding the rest of the panel. This 'six throws of the hand' rule is still code.

408.16 would seem to prohibit the split buss panels for new installations.

I guess the 'modern' use of 230.71 in residential applications would be a pair of 200A panels installed for a 400A service, without a 400A main breaker.

-Jon

Top
#58775 - 11/19/05 06:21 AM Re: No Main Disconnect on Panel?
aldav53 Offline
Member

Registered: 08/22/01
Posts: 547
Loc: Chandler, AZ USA
Yes it does have the 6 breakers on top all 240 volt with one 60a feeding the lower buss. So that serves as the 6 breaker disconnect rule? You still cannot shut down the whole panel at once, which seems to be code.

winnie, I installed a 400 amp panel a few years ago feeding a 100a from that. If I remember right, the 400a had 2-200a mains feeding a split buss. So that would take 2 mains to shut down the panel.
Art 408.16 does seem to say you cannot have more than 2 disconnects.
_________________________
The Golden Rule - "The man with the gold makes the rule"

Top
#58776 - 11/19/05 07:09 AM Re: No Main Disconnect on Panel?
mahlere Offline
Member

Registered: 11/17/05
Posts: 514
Loc: New Jersey
I believe that sec 408.16 is referring to the protection of the feeders to the appliance/lighting panelboard. (i.e. a 200A CB in the MDP prior to the feeder and then another 200A CB in the panelboard= 2 disconnects)

what should be in play here is Sec 230.71(A).

Think of it in terms of a 6 ckt MDP feeding subpanels.

Top
#58777 - 11/19/05 11:22 AM Re: No Main Disconnect on Panel?
aldav53 Offline
Member

Registered: 08/22/01
Posts: 547
Loc: Chandler, AZ USA
mahlere,
Think your right, guess they'd have to be really large appliances to exceed the main panel rating.
_________________________
The Golden Rule - "The man with the gold makes the rule"

Top
#58778 - 11/20/05 08:38 AM Re: No Main Disconnect on Panel?
DougW Offline
Member

Registered: 06/08/03
Posts: 1083
Loc: North Chicago, IL
One of the guys at the FD says he doensn't have a main D/C on his resi panel either... IIRC, the house dates back to the late 50's - early 60's.

I offered to take a look (for free, since he's a co-worker) and offer some constructive advice, but he'd rather just sit around and gripe about it.