The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by twh
Today at 06:28 AM
On Delay Relay with Auto Reset
by Potseal
Yesterday at 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
0 registered (), 192 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#58767 - 11/17/05 07:25 PM wiring a 3phase convt. to air handler/condensor
bot540 Offline
Member

Registered: 09/14/04
Posts: 177
Loc: Vernon Hills, IL
I need to wire to roof top condensor units and an air handler on two 3phase convertors. My boss provided me with a 7.5hp phase convertor and there was already a 15hp unit there already powering a unit not in use anymore.
I was going to pull #8's to the 15hp unit and feed one condensor unit(20 amps)and the airhandler with #10s. The air handler is single phase and draws about 5 amps but has a 3 phase heating element in it that draws 20 amps.
I'm going to put in a fused disconnect for each,40 amps for the convertor and 30 for the airhandler and 30 for the condensor)
I was then going to use the 7.5hp convertor for the other condensor unit. Fused 30 amps at the panel and at the fused disconnect for the convertor. I was planning on using a non-fused disconnect at the condensor and was going to pull #10s.
On both condensors it says max fuse size 30 amps.
Does this installation sound correct? I already have read article 455 and want to make sure I wire this correctly.
_________________________
Jesus may have been a capenter,but God was an electrician.Genesis1:3

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#58768 - 11/17/05 07:28 PM Re: wiring a 3phase convt. to air handler/condensor
bot540 Offline
Member

Registered: 09/14/04
Posts: 177
Loc: Vernon Hills, IL
Here is a pdf file if this helps.
http://www.phase-a-matic.com/PDF/RPL-2005-C.pdf