If you already upsized the wire for voltage drop would you have to further derate the wire if you have more than 4 current carrying conductors? Do the calculations compound?


Jesus may have been a capenter,but God was an electrician.Genesis1:3
Joined: Jul 2005
Posts: 33
C
Cow Offline
Member

Joined: Feb 2002
Posts: 182
B
Bob Offline
Member
First caculate the load.
Size the wire for the load.
Derate per the table 80%. This will give you a larger conductor. Caculate the VD using this conductor.
If you have to go larger you do not derate again.