The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Live Chat Feature
by Admin
40 minutes 47 seconds ago
Safety at heights?
by gfretwell
Today at 07:16 PM
failed home inspection.
by gfretwell
Today at 07:03 PM
Webmaster > Admin
by Admin
Today at 05:49 PM
Old Bath Fan
by gfretwell
Today at 01:38 AM
New in the Gallery:
Desk-mounted "power-board"
Top Posters (30 Days)
Admin 33
HotLine1 21
Ruben Rocha 16
gfretwell 15
Trumpy 13
Who's Online
1 registered (Admin), 0 Guests and 184 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#58573 - 11/12/05 04:52 PM Hot Tub GFCI Breaker 240v
Cinner Offline
Member

Registered: 12/01/04
Posts: 77
Loc: Kelowna, B.C., Canada
I am doing a 40 amp 2 pole gfci breaker install for a hot tub that needs only 240v. The gfci breaker has 2 neutral terminals which I understand, but in this install there is no neutral needed. Will the gfci monitor an imbalance b/w the 2 hots?

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#58574 - 11/12/05 05:06 PM Re: Hot Tub GFCI Breaker 240v
stamcon Offline
Member

Registered: 03/24/01
Posts: 322
Loc: So San Francisco CA
If the tub manufacturer states a grounded conductor(neutral) is not required, connect the line side white wire on the breaker to the neutral bus and leave the load side neutral terminal empty. The breaker will work as designed.