#58539 - 11/12/05 10:36 AM 138 Kv clearence
Alan Nadon Offline
Member
Registered: 03/10/05
Posts: 399
Loc: Elkhart, IN. USA
I need some help from line men or eng. familiar with high voltage on this question.

An installation is going in that has 138 Kv primary service. There are uninsulated bus tubes (bars) from the disconnect switch arms to the top of the distribution panel. The bus tubes are four feet apart until the get to the top of the equipment and then they are reduced to being only 8 inches apart where they enter.
The bus bars inside the equipment is insulated, the ones coming in are bare.
Outside they are exposed to the elements, i. e. snow, rain, etc.

Is 8 inches of clearence enough at 138 Kv. ??

This is a customer owned installation and I can't find this in the NEC. Would the Life Safety Code have it ?
Any good formulas on clearence or sites would be appreciated.
Thanks.
Alan--Inspector
_________________________
Alan--
If it was easy, anyone could do it.
Top
Work Gear for Electricians and the Trades
#58540 - 11/12/05 10:48 AM Re: 138 Kv clearence
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
How about the NESC?
National Electrical Safety Code.
Top
#58541 - 11/12/05 01:52 PM Re: 138 Kv clearence
royal12136 Offline
Member
Registered: 10/29/05
Posts: 20
Loc: Shasta Lake, CA USA
Hi Alan,
So far all I can find is this: http://www.pjm.com/planning/to-standards/downloads/20020520-va-general-criteria.pdf
On page 11, Table 1 under spacers, it say's 18" spacing, no preformed wire spacers allowed. This is for on the poles, but it should be the same for your situation.
Hope this helps,
Tim
Top
#58542 - 11/12/05 06:53 PM Re: 138 Kv clearence
WFO Offline
Member
Registered: 09/03/05
Posts: 202
Loc: Cat Spring, TX
Are you saying 138 KV or 13.8 Kv?

8 inches isn't nearly enough at 138 KV.
Top
#58543 - 11/13/05 07:56 AM Re: 138 Kv clearence
Alan Nadon Offline
Member
Registered: 03/10/05
Posts: 399
Loc: Elkhart, IN. USA
WFO
It is 138 Kv that is 138,000 Volts !

That is what has me asking. I don't think an eight inch clearence is enough. But, I don't know how much it should be, especially the clearence between bare conductors exposed to the elements.
This stuff is on the border between electricity and lightning.
If I'm going to challenge the spacing I need a reference. I'll check out Royal's reference it is a start.
Alan--
_________________________
Alan--
If it was easy, anyone could do it.
Top
#58544 - 11/14/05 04:06 PM Re: 138 Kv clearence
zorinlynx Offline
Member
Registered: 01/22/05
Posts: 14
Loc: Miami
Curiosity killed the cat, but...

What sort of facility uses so much power that 138kV is required to feed it? I mean, we're talking *transmission* level voltage here! Scary stuff.

-Z
Top
#58545 - 11/19/05 02:10 PM Re: 138 Kv clearence
royal12136 Offline
Member
Registered: 10/29/05
Posts: 20
Loc: Shasta Lake, CA USA
Alan,
What have you found out so far?
From a post from resqcapt19 on another topic we get this information: http://www.highvoltageconnection.com/articles/highvoltagespacing.pdf
And form what it looks like it is saying to me is 138 kv*3)/10000= 41.4 inches minimum spacing for bare conductors.
I hope that this helps and that I understand this properly.
Tim
Top
#58546 - 11/19/05 04:58 PM Re: 138 Kv clearence
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
Alan are you sure about the voltage?

Is it possible someone wrote or said 138 KV when they really meant 13.8 KV?

In my area 13.8 is a very common voltage for neighborhood and industrial distribution.

I agree with the others that 138 KV would be unusual for all but a few installations.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#58547 - 11/19/05 05:26 PM Re: 138 Kv clearence
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
Alan I think if you look carefully at the link I will provide you will be able to find pdf files that have the info you need.

http://www.lni.wa.gov/wisha/rules/electricalworkers/45-3.htm
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6778
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 57 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals