The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
Today at 02:39 AM
Photo Upload Tutorial
by DanK
Yesterday at 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
0 registered (), 282 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#58539 - 11/12/05 10:36 AM 138 Kv clearence
Alan Nadon Offline
Member

Registered: 03/10/05
Posts: 398
Loc: Elkhart, IN. USA
I need some help from line men or eng. familiar with high voltage on this question.

An installation is going in that has 138 Kv primary service. There are uninsulated bus tubes (bars) from the disconnect switch arms to the top of the distribution panel. The bus tubes are four feet apart until the get to the top of the equipment and then they are reduced to being only 8 inches apart where they enter.
The bus bars inside the equipment is insulated, the ones coming in are bare.
Outside they are exposed to the elements, i. e. snow, rain, etc.

Is 8 inches of clearence enough at 138 Kv. ??

This is a customer owned installation and I can't find this in the NEC. Would the Life Safety Code have it ?
Any good formulas on clearence or sites would be appreciated.
Thanks.
Alan--Inspector
_________________________
Alan--
If it was easy, anyone could do it.

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#58540 - 11/12/05 10:48 AM Re: 138 Kv clearence
Redsy Offline
Member

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
How about the NESC?
National Electrical Safety Code.

Top
#58541 - 11/12/05 01:52 PM Re: 138 Kv clearence
royal12136 Offline
Member

Registered: 10/29/05
Posts: 20
Loc: Shasta Lake, CA USA
Hi Alan,
So far all I can find is this: http://www.pjm.com/planning/to-standards/downloads/20020520-va-general-criteria.pdf
On page 11, Table 1 under spacers, it say's 18" spacing, no preformed wire spacers allowed. This is for on the poles, but it should be the same for your situation.
Hope this helps,
Tim

Top
#58542 - 11/12/05 06:53 PM Re: 138 Kv clearence
WFO Offline
Member

Registered: 09/03/05
Posts: 206
Loc: Cat Spring, TX
Are you saying 138 KV or 13.8 Kv?

8 inches isn't nearly enough at 138 KV.

Top
#58543 - 11/13/05 07:56 AM Re: 138 Kv clearence
Alan Nadon Offline
Member

Registered: 03/10/05
Posts: 398
Loc: Elkhart, IN. USA
WFO
It is 138 Kv that is 138,000 Volts !

That is what has me asking. I don't think an eight inch clearence is enough. But, I don't know how much it should be, especially the clearence between bare conductors exposed to the elements.
This stuff is on the border between electricity and lightning.
If I'm going to challenge the spacing I need a reference. I'll check out Royal's reference it is a start.
Alan--
_________________________
Alan--
If it was easy, anyone could do it.

Top
#58544 - 11/14/05 04:06 PM Re: 138 Kv clearence
zorinlynx Offline
Member

Registered: 01/22/05
Posts: 14
Loc: Miami
Curiosity killed the cat, but...

What sort of facility uses so much power that 138kV is required to feed it? I mean, we're talking *transmission* level voltage here! Scary stuff.

-Z

Top
#58545 - 11/19/05 02:10 PM Re: 138 Kv clearence
royal12136 Offline
Member

Registered: 10/29/05
Posts: 20
Loc: Shasta Lake, CA USA
Alan,
What have you found out so far?
From a post from resqcapt19 on another topic we get this information: http://www.highvoltageconnection.com/articles/highvoltagespacing.pdf
And form what it looks like it is saying to me is 138 kv*3)/10000= 41.4 inches minimum spacing for bare conductors.
I hope that this helps and that I understand this properly.
Tim

Top
#58546 - 11/19/05 04:58 PM Re: 138 Kv clearence
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
Alan are you sure about the voltage?

Is it possible someone wrote or said 138 KV when they really meant 13.8 KV?

In my area 13.8 is a very common voltage for neighborhood and industrial distribution.

I agree with the others that 138 KV would be unusual for all but a few installations.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#58547 - 11/19/05 05:26 PM Re: 138 Kv clearence
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
Alan I think if you look carefully at the link I will provide you will be able to find pdf files that have the info you need.

http://www.lni.wa.gov/wisha/rules/electricalworkers/45-3.htm
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts