#58356 - 11/07/05 01:58 PM Backfed Photocell?
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
A photocell will operate a lighting contactor. If I install a switch to bypass the photocell and energize the contactors coil, the bypass switchleg will also (back)feed into (red) photocell output leg.
Is this a concern?

Thanks.
Top
Work Gear for Electricians and the Trades
#58357 - 11/07/05 02:03 PM Re: Backfed Photocell?
Dnkldorf Offline
Member
Registered: 12/12/04
Posts: 1064
Loc: nowhere usa
Not for me....

It is the same phase, right?

Your not really backfeeding it, your applying the same phase on the red wire, as if the photo cell was operating properly.


Dnk.........
Top
#58358 - 11/07/05 02:06 PM Re: Backfed Photocell?
ShockMe77 Offline
Member
Registered: 06/11/05
Posts: 821
Loc: Rahway, New Jersey
Not if its on the same phase. I've wired motion detector lights like this in the past. When the light switch is on, obviously the lights are on. When the switch is off, the motion feature controls the light. I think what you are describing is the same thing.
Top
#58359 - 11/07/05 02:09 PM Re: Backfed Photocell?
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
I do not see any code issue with it.

However another option would be the use of a 3 way switch (SPDT)

Common to contactor coil.

One terminal from constant feed.

One terminal from red of the photo cell.

You end up with ON or AUTO with this set up and no back feed to the red of the cell.

Make sure the EGC is large enough.

Bob

[This message has been edited by iwire (edited 11-07-2005).]
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#58360 - 11/07/05 02:40 PM Re: Backfed Photocell?
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
Thanks guys.

The phasing is OK.
I think I actually did this configuration once before, but I'm not sure.
My concern is damaging the photocell.

iwire,

EGC, what's a EGC?




[This message has been edited by Redsy (edited 11-07-2005).]
Top
#58361 - 11/07/05 05:44 PM Re: Backfed Photocell?
capt al Offline
Member
Registered: 06/20/04
Posts: 206
Loc: Norton, Ma USA
EGC = Equipment Grounding Conductor.

Al
Top
#58362 - 11/07/05 06:14 PM Re: Backfed Photocell?
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5316
Loc: Blue Collar Country
Not a problem. I usually do this very thing.

You are not "back feeding" the photocell. The photocell is nothing more than a switch. It does not draw any current.
Top
#58363 - 11/07/05 07:11 PM Re: Backfed Photocell?
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
Thanks again guys.



[This message has been edited by Redsy (edited 11-07-2005).]
Top
#58364 - 11/07/05 07:56 PM Re: Backfed Photocell?
Larry Fine Offline
Member
Registered: 02/18/05
Posts: 693
Loc: Richmond, VA
Redsy, from what I understand, as long as the line (black) wire is hot, there's no harm in energizing the load (red) wire.
_________________________
Larry Fine
Fine Electric Co.
fineelectricco.com
Top
#58365 - 11/08/05 04:09 AM Re: Backfed Photocell?
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
Larry,

The line won't ALWAYS be hot when the red is fed from the bypass. Only when the timers contacts are closed.

Thanks.
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (cableguy619), 64 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals