#58199 - 11/02/05 11:47 AM Coleman 5kw generator question
Grover Offline
Member
Registered: 01/19/05
Posts: 109
Loc: Sebago, ME, USA
My customer has an older Coleman 5Kw Powermate PM0525202.

Problem is that the receptacle is different - it's got a 6-20R rather than an L14-20R (one flat and one 90deg rotated blade vs. 4 prong twistlock). I checked the Coleman site - no schematic. I assume the neutral and the GND are bonded inside the unit. There is a separate 120 v duplex on the unit.

Has anyone ever changed out the receptacle so the neutral and GND are brought out separately. I plan to back-feed the panel with a Square D interlock.

Thanks for help!
Top
Work Gear for Electricians and the Trades
#58200 - 11/02/05 05:20 PM Re: Coleman 5kw generator question
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
Coleman says it should have a twistlock. Are you sure that is the right model number?
_________________________
Greg Fretwell
Top
#58201 - 11/02/05 05:58 PM Re: Coleman 5kw generator question
davemica Offline
Member
Registered: 10/26/05
Posts: 12
Loc: florida
If you are talking about the 3 wire 240v receptacle on that generator, check carefully, as I'm pretty sure there is no midpoint neutral just straight 240v.
Top
#58202 - 11/02/05 09:28 PM Re: Coleman 5kw generator question
Grover Offline
Member
Registered: 01/19/05
Posts: 109
Loc: Sebago, ME, USA
Yup, sure of the model # - it's an older model; current models have the 4 conductor twist lock.

My custoer's unit has what appears to be 2 duplex receptacles, one marked 120V and the other marked 240V - a 5-20R and a 6-20R. Tells me there's got to be a neutral somewhere......
Top
#58203 - 11/02/05 11:00 PM Re: Coleman 5kw generator question
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
You could meter it out. If the neutral is bonded you should see 0 ohms between the neutral and ground on the NEMA 5-15s and the ground on the 6-20. To be connected properly your transfer equipment should also be switching the neutral.
_________________________
Greg Fretwell
Top

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 101 Guests and 13 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Stack, Scotto, Freecrowder, clee512, Jdscott2005

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals