The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
Yesterday at 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
0 registered (), 97 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#58063 - 10/27/05 09:20 PM Tap conductors
Tripp Offline
Member

Registered: 09/20/05
Posts: 101
There was recently a thread that dealt in part with this topic, but for the life of me I cannot find it. My question is: WHAT IS THE DEFINITION OF A TAP CONDUCTOR? I find it nowhere in the NEC. More specifically, when you terminate a #8 copper in a box for a raqnge recept, can you pigtail the grounds to a smaller AWG? Is this a "tap"?

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#58064 - 10/28/05 05:59 AM Re: Tap conductors
Ryan_J Offline
Moderator

Registered: 08/19/03
Posts: 1355
Loc: West Jordan, Utah, USA
You will find your definition in 240.2.

Also, what you describe is not a tap, it is an undersized equipment grounding conductor
_________________________
Ryan Jackson,
Salt Lake City

Top
#58065 - 10/28/05 12:27 PM Re: Tap conductors
Tesla Offline
Member

Registered: 06/16/04
Posts: 1280
Loc: Sacramento, CA
Tripp, you're hunting for table 210.24....

Also study 240.5 particularly 240.5(2)

Also study 210.19 (A)(3) exceptions #1,#2

Also study 210.19 (A)(4) exception #1 (c)

These tap conductors are limited to 18 inches.
_________________________
Tesla

Top