The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Safety at heights?
by HotLine1
Yesterday at 08:51 PM
International Wire Colour Codes
by Texas_Ranger
Yesterday at 03:29 PM
Looking for older post
by Texas_Ranger
Yesterday at 03:22 PM
Last time to chat here
by Trumpy
01/20/17 11:41 PM
Unsafe Situations
by Trumpy
01/20/17 09:46 PM
New in the Gallery:
Desk-mounted "power-board"
Shout Box

Top Posters (30 Days)
Admin 35
HotLine1 20
Ruben Rocha 17
gfretwell 16
Trumpy 15
Who's Online
1 registered (HotLine1), 165 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#58063 - 10/27/05 09:20 PM Tap conductors
Tripp Offline
Member

Registered: 09/20/05
Posts: 101
There was recently a thread that dealt in part with this topic, but for the life of me I cannot find it. My question is: WHAT IS THE DEFINITION OF A TAP CONDUCTOR? I find it nowhere in the NEC. More specifically, when you terminate a #8 copper in a box for a raqnge recept, can you pigtail the grounds to a smaller AWG? Is this a "tap"?

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#58064 - 10/28/05 05:59 AM Re: Tap conductors
Ryan_J Offline
Moderator

Registered: 08/19/03
Posts: 1355
Loc: West Jordan, Utah, USA
You will find your definition in 240.2.

Also, what you describe is not a tap, it is an undersized equipment grounding conductor
_________________________
Ryan Jackson,
Salt Lake City

Top
#58065 - 10/28/05 12:27 PM Re: Tap conductors
Tesla Offline
Member

Registered: 06/16/04
Posts: 1280
Loc: Sacramento, CA
Tripp, you're hunting for table 210.24....

Also study 240.5 particularly 240.5(2)

Also study 210.19 (A)(3) exceptions #1,#2

Also study 210.19 (A)(4) exception #1 (c)

These tap conductors are limited to 18 inches.
_________________________
Tesla

Top