The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

   
Topic Options
Rate This Topic
#57727 - 10/18/05 09:21 PM Expansion coupling...
Attic Rat Offline
Member
Registered: 12/14/03
Posts: 530
Loc: Bergen Co.,N.J. USA
... We're doing a 300 amp. underground service for a residence,and I know that I need to insert an expansion coupling,..but where?? on the line side schedule 80 pvc,just before the meter,or in the trench,...and do I also need one on the load side before entering the basement through the foundation??

I realize it depends on the length of run and the expected change in ambient temperature, but I'm a little fuzzy on where to place it...(don't be funny, I know what you're about to say..)
Russ
_________________________
.."if it ain't fixed,don't break it...call a Licensed Electrician"
Top
Work Gear for Electricians and the Trades
#57728 - 10/18/05 10:07 PM Re: Expansion coupling...
Tesla Offline
Member
Registered: 06/16/04
Posts: 1280
Loc: Sacramento, CA
Fully buried PVC is not prone to expansion issues.

The expansion joint would be needed if the length of exposed run is more than stubbing out to a panel/ meter pan.

Buried runs usually do not have expansion joints since the ground greatly moderates their temperature swings.
_________________________
Tesla
Top
#57729 - 10/19/05 05:38 AM Re: Expansion coupling...
winnie Offline
Member
Registered: 09/15/03
Posts: 652
Loc: boston, ma
Hear-say (from the photo discussion area on ECN , rather than personal experience: for a short stub of pvc from underground to the meter pan, the thermal expansion will not be enough to matter. Thermal expansion and contraction shows up as a percentage change in length, so the shorter the 'nominal' length, the smaller the change produced by thermal effects.

However the expansion joint will also nicely accommodate things like the soil settling after construction, or the earth moving for other reasons. If you search in the Photos Submitted for Discussion area, I'm sure you will find pictures of residential service stubs ripped out of meter pans by the ground settling.

-Jon
Top
#57730 - 10/19/05 07:53 PM Re: Expansion coupling...
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2209
Loc: IL
As Jon stated, ground movement is a problem that can be solved by using an expansion fitting and is one method of compliance with 300.5(J).
Don
_________________________
Don(resqcapt19)
Top
#57731 - 10/20/05 05:39 PM Re: Expansion coupling...
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6833
Loc: Brick, NJ USA
Rat:

IF you run pvc from meter pan (at house) to pole, & up the obligatory 10'; you need an expansion joint between the ma at the meter pan, and the dirt.

IF you only have to 'leave' a short pvc piece, with the bell/bushing; for BUD direct burial by utility; you do NOT need an exp. joint.

As Jon & Don said....ground heaving, not expansion in this case.

(From another Jersey Guy)

John
_________________________
John
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Forum Styles
by Admin
01/24/17 02:22 PM
License exam
by TRUE POWER
01/23/17 09:16 PM
Looking for older post
by sparkyinak
01/23/17 12:27 AM
Members: Non-Members: Did you know?
by Admin
01/22/17 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM

Who's Online
1 registered (Admin), 97 Guests and 14 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Member Since: 08/17/06
Posts: 358

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals