#57614 - 10/17/05 03:24 PM corner tapped delta  
lamplighter  Offline
Member
Joined: Oct 2005
Posts: 101
Clawson,Michigan,USA
I've only had to work with this a couple of times but, in each time, I got different answers from those that seemed "in the know".
When installing a disconnect on the secondary side of a corner tapped delta transformer, does one need to fuse the grounded leg or install a dummy fuse in the jaws?
I've been told to fuse it since it is one of the three legs going to the equipment but, it's also the grounded conductor which would mean NO FUSE.
I can't find anything in the code about this.
Any help?


Work Gear for Electricians and the Trades

#57615 - 10/17/05 03:43 PM Re: corner tapped delta  
Crowbar  Offline
Member
Joined: Jan 2003
Posts: 33
Pittsburgh, PA,USA
Being an intentionally grounded conductor would make 240.22 (2002 NEC) apply
"No overcurrent device shall be connected in series with any conductor that is intentionally grounded, unless"...(exceptions not relevant in this case)


#57616 - 10/17/05 09:16 PM Re: corner tapped delta  
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
Ditto crowbar.

A grounded conductor by any other name (neutral, or not) is a grounded conductor.
Don't forget Article 200.



[This message has been edited by Redsy (edited 10-17-2005).]


#57617 - 10/17/05 10:05 PM Re: corner tapped delta  
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
I beg to differ! On a corner grounded delta you most certainly fuse the grounded leg!
See 430.36, which specifically addresses this situation.


#57618 - 10/17/05 10:35 PM Re: corner tapped delta  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,057
Estero,Fl,usa
Reno, that is only if the fuses are the "overload" protection. That does not affect the OC device for overcurrent protection.


Greg Fretwell

#57619 - 10/18/05 06:33 PM Re: corner tapped delta  
ShockMe77  Offline
Member
Joined: Jun 2005
Posts: 821
Rahway, New Jersey
430.36 says: and also in the grounded conductor if the supply system is a 3-wire, 3 phase ac with one conductor grounded.

I'm not an expert of Delta systems, but this code in my opinion says yes, the grounded conductor must have fused protection.

[This message has been edited by ShockMe77 (edited 10-18-2005).]


#57620 - 10/18/05 07:18 PM Re: corner tapped delta  
togol  Offline
Member
Joined: Sep 2005
Posts: 421
NW In. USA
...mind if I jump in and ask... if there are any problems with two-wire single phase loads? should I not use the grounded phase on a two pole breaker ?
its been years since I worked on this type of service and I have a job moving a small shop with a single phase service to an old building with ths stuff ?
I realize I need to check the motors that are running off of converters, I just ain't sure about the 2 pole gear


Tom

#57621 - 10/18/05 07:29 PM Re: corner tapped delta  
earlydean  Offline
Member
Joined: Dec 2003
Posts: 751
Griswold, CT, USA
Read the whole section:

"430.36 Fuses — In Which Conductor.
Where fuses are used for motor overload protection, a fuse shall be inserted in each ungrounded conductor and also in the grounded conductor if the supply system is 3-wire, 3-phase ac with one conductor grounded."

There is a difference between overload protection and short circuit and ground fault protection. Motors circuits break the overcurrent protection into these two parts:
1) Short circuit and ground fault protection
2) Overload protection

We usually provide #1 with the circuit breaker protecting the feeder, and #2 with heaters in the motor starter.

At a transformer providing power to a motor control center, all the conductors need to follow the rules in Article 240.

"II. Location
240.20 Ungrounded Conductors.
(A) Overcurrent Device Required. A fuse or an overcurrent trip unit of a circuit breaker shall be connected in series with each ungrounded conductor."

"240.21 Location in Circuit.
Overcurrent protection shall be provided in each ungrounded circuit conductor and shall be located at the point where the conductors receive their supply except as specified in 240.21(A) through (G)."

And most importantly:

"240.22 Grounded Conductor.
No overcurrent device shall be connected in series with any conductor that is intentionally grounded, unless one of the following two conditions is met:
(1) The overcurrent device opens all conductors of the circuit, including the grounded conductor, and is designed so that no pole can operate independently.
(2) Where required by 430.36 or 430.37 for motor overload protection."

Fuses cannot simultaneously open all conductors of the circuit. That leaves us only (2).

The answer, then, is: unless the fuse is intended to provide the overload protection for a motor (instead of the heaters) then a fuse in the grounded conductor is not allowed. So, go ahead, install a two pole fused disconnect for your motor control center.

Does the listing on a three phase disconnect permit the installation of a six inch piece of copper pipe in place of a fuse? Or, does the manufacturer sell dummy fuses for this purpose? Or is it only proper to install a 2 pole fused disconect for this use?


Earl

#57622 - 10/18/05 07:59 PM Re: corner tapped delta  
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA



Member Spotlight
Attic Rat
Attic Rat
Bergen Co.,N.J. USA
Posts: 524
Joined: December 2003
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.014s Queries: 14 (0.002s) Memory: 0.8005 MB (Peak: 0.9658 MB) Zlib enabled. Server Time: 2017-03-25 03:59:00 UTC