#57420 - 10/14/05 01:33 PM sub panel
drgnz23 Offline
Member
Registered: 02/17/02
Posts: 56
Loc: los angeles
Im going crazy! I swore i read something in ECM mag that a sub panel in a detttached garage must have a separate ground rod . Is this true or im i mistaken?
Top
Work Gear for Electricians and the Trades
#57421 - 10/14/05 01:45 PM Re: sub panel
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
Yes that is correct, take a look at 225.30 through 225.40 for all the requirements that you will need to follow for a detached garage panel.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#57422 - 10/15/05 05:21 AM Re: sub panel
harold endean Offline
Member
Registered: 02/16/02
Posts: 2233
Loc: Boonton, NJ
Bob,

I read on another web site that it is also useful in case of lightning. You want the lightning to disapate in the earth by the garage in stead of trying to get back to the main house.
Top
#57423 - 10/15/05 07:44 PM Re: sub panel
drgnz23 Offline
Member
Registered: 02/17/02
Posts: 56
Loc: los angeles
Thanks fellas . I knew i read something about that
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6775
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 14 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals