#57413 - 10/14/05 05:56 AM Flood Zone Requirements
GamecockEE Offline
Member
Registered: 07/28/04
Posts: 49
Loc: Georgetown, SC 29440
I am doing some engineering research for the electrical renovation of an existing early 1980's vintage, 8 story, ocean-front high rise hotel. The owner is converting it to time share condominium uses.
My question is about what electrical equipment is allowed below the base flood elevation, what equipment is required to be above this level, and what Code, or governmental regulatory standard addresses these issues. Thanks for the input
Top
Work Gear for Electricians and the Trades
#57414 - 10/14/05 07:47 AM Re: Flood Zone Requirements
earlydean Offline
Member
Registered: 12/22/03
Posts: 749
Loc: Griswold, CT, USA
FEMA will identify flood hazardous areas. Local building code will tell construction methods. Local zoning will adopt the FEMA standards. Electrical equipment below the flood zone will be in a wet location, and all equipment will have to be gasketed and watertight. What we usually do is to build the house on stilts, and keep all electrical equipment above the flood level. Any wiring below has to have a "W" in the insulation.
_________________________
Earl
Top
#57415 - 10/14/05 08:38 AM Re: Flood Zone Requirements
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9066
Loc: Estero,Fl,usa
If it was really true that anything below flood plain was required to be "water tight" I would need gasketed boxes in my living room. (FF is at 9' above sea level.)
They don't do anythinbg special in South Florida. If the wiring is outside it gets done the same as any other outside wiring. If the area is a "utility space" (a euphamism for living space below flood) it uses normal inside wiring methods.
In Florida "flood" is <11' above sea level. On a piling house it is very common to have the bottom floor enclosed with "blow out" walls and calling it utility space. They get wired with romex and blue Carlon nail ups.
_________________________
Greg Fretwell
Top
#57416 - 10/14/05 09:35 AM Re: Flood Zone Requirements
earlydean Offline
Member
Registered: 12/22/03
Posts: 749
Loc: Griswold, CT, USA
and after every flood all the wiring below has to be replaced.
_________________________
Earl
Top
#57417 - 10/14/05 09:38 AM Re: Flood Zone Requirements
macmikeman Offline
Member
Registered: 07/16/02
Posts: 718
Loc: Honolulu, Hawaii
In Honolulu, the requirement is to make all circuits below the fz level be protected by a gfi. So like South Florida, most new houses in the defined flood zone are up on stilts and the outlets and switches and so forth that are at grade level, have to be gfi protected. Where this whole thing is retarted is that the poco still demands the meter/main to be 5-6' ft high off of grade level, which I think sort of negates any branch circuit protection if the water levels get over the height of the meter/main can.
Top
#57418 - 10/15/05 05:26 AM Re: Flood Zone Requirements
harold endean Offline
Member
Registered: 02/16/02
Posts: 2248
Loc: Boonton, NJ
In NJ, new construction needs all mech equip. to be installed above Fz area. It is common to see HVAC units on 2nd floor decks, on roofs, or on raised platforms. We are having flooding rains yesterday and today as we speak in one of the towns that I inspect. As for equipment that goes under water, it has to be re-examined by a listing agency or replaced. An EC can give a letter saying that it is OK, but I don't know of many that will do that.
Top
#57419 - 10/16/05 06:23 PM Re: Flood Zone Requirements
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9066
Loc: Estero,Fl,usa
Mike is talking about vitrtually the same rules as they have here. On a piling house the meter can is going to be at grade. That reader is not climbing stairs all day. They won't move the bushes over.
The GFCI (remember "utility area")sort of negates the idea of "replacing all the wiring" after a flood. If it holds the GFCI it is dry "enough".
_________________________
Greg Fretwell
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Looking for older post
by sparkyinak
Today at 12:27 AM
License exam
by TRUE POWER
Yesterday at 11:33 PM
Members: Non-Members: Did you know?
by Admin
Yesterday at 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM
International Wire Colour Codes
by Texas_Ranger
01/21/17 03:29 PM

Who's Online
1 registered (Admin), 89 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Member Since: 08/01/07
Posts: 62

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals