The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
0 registered (), 198 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#57410 - 10/13/05 07:12 PM Switchgear used as raceway?
bot540 Offline
Member

Registered: 09/14/04
Posts: 177
Loc: Vernon Hills, IL
I am installing a 800A panel off an exsisting switchgear in a renovated hotel.
The MDP is set up for two services on the left is a 1600 service for the heat/ac and on the right is a 1200 service for general power(receptacles,lights,ect.) In the center is where the parallel service conductors enter the gear.
The problem is that we piped 3 3"(underground) to the right side of the gear. Well we got the breaker in, Square D and it will only fit on the left side of the gear. My boss wants me to run the conductor feeding the 800a panel through the center,(passing the service conductors to the left side of the gear. I am guessing that this is in violation of article 230.7 . Am I correct?
_________________________
Jesus may have been a capenter,but God was an electrician.Genesis1:3

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#57411 - 10/14/05 03:58 AM Re: Switchgear used as raceway?
Tom Offline
Member

Registered: 01/01/01
Posts: 1069
Loc: Shinnston, WV USA
I believe that your understanding of 230.7 is correct.

Can you install conduit nipples through the middle compartment or can a metal divider be installed in the compartment to separate service from non-service conductors? Otherwise, you'll have to get creative with elbows & condulets and come out the sides or top & pipe over to the other side.
_________________________
Few things are harder to put up with than the annoyance of a good example.

Top
#57412 - 10/14/05 03:23 PM Re: Switchgear used as raceway?
bot540 Offline
Member

Registered: 09/14/04
Posts: 177
Loc: Vernon Hills, IL
I,m afraid it's not going to be that easy. We.re still thinking up a solution.
_________________________
Jesus may have been a capenter,but God was an electrician.Genesis1:3