#57181 - 10/06/05 02:40 PM New Transfer switch for portable generators
Dnkldorf Offline
Member
Registered: 12/12/04
Posts: 1064
Loc: nowhere usa
What do you guys think of these, pros and cons welcome...
http://www.globalpowerproducts.com/generlink.htm


Dnk.......
Top
Work Gear for Electricians and the Trades
#57182 - 10/06/05 03:00 PM Re: New Transfer switch for portable generators
raider1 Offline
Member
Registered: 07/08/05
Posts: 46
Loc: north logan, utah, US
I think it might be hard to get the utility company to buy off on it.

Chris
Top
#57183 - 10/06/05 03:06 PM Re: New Transfer switch for portable generators
DSpanoudakis Offline
Member
Registered: 08/31/05
Posts: 89
Loc: Astoria, Queens, N.Y.C.
Sounds to be easier for power theft.
Top
#57184 - 10/06/05 03:20 PM Re: New Transfer switch for portable generators
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
What about the bonding issues pertaining to the generators neutral?
How does this switch work?
Top
#57185 - 10/06/05 03:29 PM Re: New Transfer switch for portable generators
Tesla Offline
Member
Registered: 06/16/04
Posts: 1273
Loc: Sacramento, CA
I'm confused....

Just what problem is solved by this device?

Their blurb indicates that it can be installed by the utility in less than 30 minutes.

So?

It apparently has internal logical control which cuts line from load whenever it senses alternate power flowing in.

I don't see a market for his device.
_________________________
Tesla
Top
#57186 - 10/06/05 04:09 PM Re: New Transfer switch for portable generators
Dnkldorf Offline
Member
Registered: 12/12/04
Posts: 1064
Loc: nowhere usa
Does anyone see a UL listing for this?


Dnk...
Top
#57187 - 10/06/05 06:06 PM Re: New Transfer switch for portable generators
ShockMe77 Offline
Member
Registered: 06/11/05
Posts: 821
Loc: Rahway, New Jersey
I think this thing stinks because it cuts in to our labor hours. How long does it take to wire one of these, 30 minutes?
Top
#57188 - 10/07/05 07:42 PM Re: New Transfer switch for portable generators
sierra electrician Offline
Member
Registered: 02/12/05
Posts: 219
Loc: North Fork, CA USA
There is no way the POCO in our area would install this device. They are simply not set up for this type of Customer Service.

Rob
Top
#57189 - 10/08/05 04:16 AM Re: New Transfer switch for portable generators
earlydean Offline
Member
Registered: 12/22/03
Posts: 751
Loc: Griswold, CT, USA
I see in the installation instructions that they use a split bolt (split nut) connection to tie into the neutral at the meter can. The pic clearly shows a copper only split bolt connected to aluminum wires.
This aside, anything before the first means of disconnect is service equipment. As such, this device must be rated for service use. Nowhere, that I could find is this device UL or CSA tested, listed and approved.
Also, as has been stated, this device is a clear means of eliminating the electrician from the installation. I know I am biased, but, elimination of the electrician is always a recipe for disaster. The service wires coming in have no O.C. protection. Homeowners should never be allowed to mess with them.
_________________________
Earl
Top
#57190 - 10/08/05 04:40 AM Re: New Transfer switch for portable generators
earlydean Offline
Member
Registered: 12/22/03
Posts: 751
Loc: Griswold, CT, USA
Did you folks know that, generally speaking, portable generators cannot legally be connected to the internal wiring of any building?

Most all portable generators have the neutral and ground wires bonded together. It is required to bond the frame of the generator to the equipment grounding conductor (250.4). It is also required to run a separate conductor for the neutral (250.30). The utility power source, at the service, has the neutral and equipment ground bonded together (250.26). There is no way to avoid having a parallel path on the conductors that carry the neutral and the equipment ground to the portable generator: they are bonded permanently at both ends (violation of 250.30(A)(1)).
Only a hard wired generator with the neutral NOT bonded to the frame is acceptable as a standby or emergency generator. Most all portable generators have this bonding done at the factory and they cannot be undone. Portable generators are to be used only for cord connected loads, plugged into the outlets provided at the generator.
_________________________
Earl
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 04/03/02
Posts: 6776
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (annemarie1), 67 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals