#57110 - 10/05/05 12:19 AM Detached Garage
Sparks30 Offline
Member
Registered: 03/23/02
Posts: 125
Loc: Connecticut.usa
I will be brining 3 circuits to the garage through a 1" PVC. It is about 20' from the house. Do i need disconnecting means for these circuits?
Top
Work Gear for Electricians and the Trades
#57111 - 10/05/05 02:53 AM Re: Detached Garage
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
Sparks you really can't run three circuits to a detached building.

Quote:
225.30 Number of Supplies.
Where more than one building or other structure is on the same property and under single management, each additional building or other structure served that is on the load side of the service disconnecting means shall be supplied by one feeder or branch circuit unless permitted in 225.30(A) through (E). For the purpose of this section, a multiwire branch circuit shall be considered a single circuit.


There are some allowances for more than one circuit but it is unlikely they will fit for you.

You need to look at 225.30 to 225.40

You need disconnects and grounding electrodes. If you have to have three circuits you will be installing a feeder with a panel at the garage.

Is it possible you could do it with just two circuits?

One multiwire branch circuit will provide two circuits and does not require the grounding electrode.

Bob
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#57112 - 10/05/05 11:55 AM Re: Detached Garage
Sparks30 Offline
Member
Registered: 03/23/02
Posts: 125
Loc: Connecticut.usa
I can do it with 2. I was tring to give then 2 power an 1 lighting. Now it will be a 12-3 circuit. Thanks for the help.
Top
#57113 - 10/05/05 07:13 PM Re: Detached Garage
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9036
Loc: Estero,Fl,usa
Since the final stretch is only 20' or so, run it in #10-3. That way if they do outgrow your 20a multiwire you can put a 2/4 box in there and give them 4 circuits or 2 and a double pole 240 with minimal hassle.
_________________________
Greg Fretwell
Top
#57114 - 10/05/05 08:47 PM Re: Detached Garage
ShockMe77 Offline
Member
Registered: 06/11/05
Posts: 821
Loc: Rahway, New Jersey
Heck, if it was up to me, I'd definitely be doing a sub panel. If the owner needs power out there now, who knows what else he'll be adding in the future. It would suck to have to dig another trench when you could have done right the first time. The "ka-ching" portion of the job is also nice.

Good luck.
Top
#57115 - 10/07/05 12:18 AM Re: Detached Garage
Sparks30 Offline
Member
Registered: 03/23/02
Posts: 125
Loc: Connecticut.usa
Thanks for the replys. I most likly will go with the 10 wire. H.O want cheap. Doing 2 garage door outlet, 6 porcelin, 1 outside light and 8 outlets.
Top

Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 51 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 79
HotLine1 51
Ruben Rocha 29
gfretwell 25
Trumpy 20
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals