The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
Today at 02:39 AM
Photo Upload Tutorial
by DanK
Yesterday at 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
1 registered (LongRunner), 218 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#5696 - 12/01/01 09:18 PM Flexible metallic conduit for grounding purposes??
duanet Offline
Junior Member

Registered: 12/02/01
Posts: 7
Is it an accepted standard to use flexible metallic conduit (in a two wire single phase branch circuit -no separate ground wire-)Is it o.k. to use the flex as ground? Or does it have to be EMT? I am tying in some older (2 wire-hot/common EMT as ground)) Circuits to a new load center and wish to no if this is proper by NEC standards. i want to use flex for the new offsets the circuits have to make.

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#5697 - 12/02/01 09:01 AM Re: Flexible metallic conduit for grounding purposes??
Nick Offline
Member

Registered: 08/13/01
Posts: 603
Loc: Riverside, CA
Is it an accepted standard? In my experience, no. Is it NEC compliant? Yes, provided the ground fault return path is 6ft or less and the fittings and flex you use are listed for grounding. Note that the 6ft. or less is for the entire run of the circuit. For example, you cannot run a piece of conduit with a 6ft flex whip into the panel on one end and a 6ft. whip to a fixture on the other end. That would be a fault return of 12ft. I think most here will agree either keep the run in EMT or pull an equipment grounding conductor.

Top
#5698 - 12/07/01 09:30 PM Re: Flexible metallic conduit for grounding purposes??
Steve T Offline
Member

Registered: 02/14/01
Posts: 312
Loc: Oak Park, IL, USA
Nick,

Flexible metal conduit not listed for grounding can be used as a ground provided it is less than 6 feet and the fittings are listed for grounding and the circuits are protected at 20 amps or less and it is not installed for flexibility.

Flexible metal conduit listed for grounding can be any length provided the fittings are also listed for grounding.

By the way, has anyone seen how much the UL description of flex fittings listed for grounding and flex fittings not listed for grounding has changed from the 1999 book to the 2000 book? It is quite significant. There appears to be no special determination for steel vs. aluminum using set screw type connectors in the 2000 book like there was in the 1999 book.

Top
#5699 - 12/08/01 06:57 PM Re: Flexible metallic conduit for grounding purposes??
electure Offline

Member

Registered: 12/24/00
Posts: 4226
Loc: Fullerton, CA USA
Can you provide us with some of the manufacturers that have this listed combination sans ground wire??

I'd like to use them!

Top
#5700 - 12/11/01 04:30 PM Re: Flexible metallic conduit for grounding purposes??
Steve T Offline
Member

Registered: 02/14/01
Posts: 312
Loc: Oak Park, IL, USA
electure

I'm not sure I understand what you are looking for. Listed flexible metal conduit?