The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
Yesterday at 08:46 PM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
ghost307 7
HotLine1 7
renosteinke 6
Potseal 4
Who's Online
0 registered (), 299 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#5685 - 12/01/01 06:27 PM services
mar1961 Offline
Junior Member

Registered: 11/28/01
Posts: 2
Loc: Wheeling,WV,USA
I just bought a very old house that had recently been rewired into three diferent apartments . My wife and I decided to make it into one house again my problem is I have three diferent pannels , three different meter-cans, and three different electric bills.
My question is what is the most economical way to make it just one service?

Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#5686 - 12/02/01 06:09 AM Re: services
ken m Offline

Registered: 08/14/01
Posts: 61
Loc: south carolina
if it is not too much of a problem paying 3 different bills that would be the less expensive way out. otherwise you would have to, depending on your location, remove the 3 meter bases and install 1 meterbase\breaker combo with at least 6 bkr spaces and feed the 3 separate bkr panels from there. that is if the feeders are long enough. if not the cost just keeps rising. if your wanting to consolidate the 3 bkr panels into 1 then your looking at some serious re-wiring.
hope some of this helps. ken m

#5687 - 12/02/01 01:10 PM Re: services
electure Offline


Registered: 12/24/00
Posts: 4226
Loc: Fullerton, CA USA
To meet Code you will not be able to keep 3 meters in 1 occupancy per 230-40. 1 occupancy=1 meter. (Sorry)
I think the least expensive code compliant option you have is to sub-feed the 2 other panels from your main service panel, which will need to be sized to the entire load of your house.
You'll also have to abandon the 2 extra service grounds.

[This message has been edited by electure (edited 12-02-2001).]


ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals