The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
Yesterday at 09:52 PM
International Wire Colour Codes
by Texas_Ranger
Yesterday at 08:24 AM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 12
HotLine1 6
renosteinke 6
ghost307 5
Potseal 4
Who's Online
2 registered (Tjia1981, sparkyinak), 236 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#56847 - 10/01/05 09:28 AM Reliance Control Transfer panel ?
Grover Offline

Registered: 01/19/05
Posts: 110
Loc: Sebago, ME, USA
Does anyone have experience with the Reliance TCA1003D transefer switch?

I've looked for details, and can't seem to find any. It it really a 100A/30A breaker in a box - mechanically interlocked? So in operation it becomes a "whole house feed", and the homeowner has to figure out what he can and cannot use.

Also, this means I've got to get the PoCo involved to install it (kill the feed), right?

Thanks for info!

Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#56848 - 10/01/05 12:50 PM Re: Reliance Control Transfer panel ?
Dave T Offline

Registered: 01/22/05
Posts: 157
Loc: Waukesha, WI, USA

#56849 - 10/01/05 12:53 PM Re: Reliance Control Transfer panel ?
Larry Fine Offline

Registered: 02/18/05
Posts: 684
Loc: Richmond, VA
Yes, this is merely a 4-space CH main-lug panel with two breakers mechanically interlocked. The generator feeds the 30-a breaker terminals, back-feed style, and the utility the 60-a breaker likewise. The main lugs feed the load.

This assembly must be rated "suitable for use as service equipment" unless you add a main breaker between it and the meter. In addition, this unit can not be used in this manner on a service greater than 60 amps.

This panel is more suited to feed a sub-panel that supplies loads desired to be generator-powered, and not an entire premises. Additionally, back-fed breakers are supposed to have a "hold-down" device installed.

I have made my own transfer panels by basically combining this panel and a sub-panel by using a pair of breakers this same way, but in a panel large enough to contain the two "main" breakers and the branch circuits.

[This message has been edited by Larry Fine (edited 10-01-2005).]
Larry Fine
Fine Electric Co.

#56850 - 10/02/05 05:00 AM Re: Reliance Control Transfer panel ?
Grover Offline

Registered: 01/19/05
Posts: 110
Loc: Sebago, ME, USA
Thanks Larry

It's what I suspected.....

Any experience with the company that makes an "add in" mechanical interlock for generator applications? I saw a website a while ago that was selling Reliance-like interlocks made for several different panels.

What I'm looking for is a real cost-effective solution to backfed panels I keep coming across out here in the woods of Maine......

#56851 - 10/02/05 06:57 AM Re: Reliance Control Transfer panel ?
Ron Offline

Registered: 03/13/02
Posts: 577
Loc: White Plains, NY
I have a reliance controls panel in my own home. TTV2003D Panel/Link.
It seems really well made and rugged.
You can purchase breaker interlocks if you have a Square D panel.