The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Safety at heights?
by HotLine1
Yesterday at 08:51 PM
International Wire Colour Codes
by Texas_Ranger
Yesterday at 03:29 PM
Looking for older post
by Texas_Ranger
Yesterday at 03:22 PM
Last time to chat here
by Trumpy
01/20/17 11:41 PM
Unsafe Situations
by Trumpy
01/20/17 09:46 PM
New in the Gallery:
Desk-mounted "power-board"
Shout Box

Top Posters (30 Days)
Admin 35
HotLine1 21
Ruben Rocha 17
gfretwell 16
Trumpy 15
Who's Online
1 registered (Admin), 67 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#5658 - 11/29/01 04:51 PM GFI - spa circuit
aldav53 Offline
Member

Registered: 08/22/01
Posts: 547
Loc: Chandler, AZ USA
I previously ran a 50a circuit for a spa and it had no place for a neutral at the spa end, so I did'nt run one. I put in a 50a GFI breaker (not using a neutral) and tested the GFI hot to ground on both legs at the spa and it worked, the GFI did trip fine. Was I wrong for not running a neutral? Even though it trips ok? I'm not sure why this works since GFI's use the nuetral and ground.
_________________________
The Golden Rule - "The man with the gold makes the rule"

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#5659 - 11/29/01 07:10 PM Re: GFI - spa circuit
Nick Offline
Member

Registered: 08/13/01
Posts: 603
Loc: Riverside, CA
If the spa did not require a neutral then there are no line to neutral loads. The GFCI breaker is seeing equal balance between the phases and thinks life is rosy. When you connect a phase to ground current flows outside the ground fault circuitry, it sees an imbalance, and trips. No you do not need the neutral. Where would you terminate it?

Top
#5660 - 11/29/01 07:39 PM Re: GFI - spa circuit
aldav53 Offline
Member

Registered: 08/22/01
Posts: 547
Loc: Chandler, AZ USA
Duh, It just hit me, that makes total sense.
Thanks,