#56217 - 09/16/05 11:46 PM Armored cable in the Barn?
steve 2003 Offline
Member
Registered: 03/16/03
Posts: 9
Loc: san clemente, ca US...
Is it code to use armored cable in a barn, and use plastic junction boxes? Its all open wall and ceiling,I was going to use the 12-3 armored for all the runs split the 12-3 for the lights and outlets then use two breakers for that whole run.
Top
Work Gear for Electricians and the Trades
#56218 - 09/17/05 02:11 AM Re: Armored cable in the Barn?
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
As you said barn it may well be an agricultural building per 547.1(A) and (B).

If it is an agricultural building steel jacketed AC cable is out of the question.

Also and more importantly, plastic boxes with steel cables and raceways are a very bad idea.

At the least you should read Article 547.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#56219 - 09/17/05 06:30 AM Re: Armored cable in the Barn?
classicsat Offline
Member
Registered: 11/23/02
Posts: 456
Where I am at (Ontario Canada), standard practice in older wooden/open frame agricultrural buildings is NMW-10 cable (AKA UF-B), and surface mount bakelite fittings. New er "closed frame" barns will have PVC conduit and fittings. The service panel is either in a "doghouse" on the outside of the barn, or in an anteroom or mechancial room sealed from where the livestock is kept.
Top
#56220 - 09/17/05 07:04 AM Re: Armored cable in the Barn?
Mvannevel Offline
Member
Registered: 03/19/03
Posts: 29
Loc: Hesperia, Michigan, USA
If this is an agricultural building as described in 547.1(A) or (B), MC cable would be allowable but definitely not AC. And if MC cable were used, plastic boxes would have to meet the exceptions to 314.3, otherwise they are not permitted with metal raceways or metal-armored cables.
Top
#56221 - 09/17/05 07:36 AM Re: Armored cable in the Barn?
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
That MC would have to have a plastic jacket as well.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#56222 - 09/17/05 09:10 AM Re: Armored cable in the Barn?
steve 2003 Offline
Member
Registered: 03/16/03
Posts: 9
Loc: san clemente, ca US...
This barn is all wood has two horses in there own stalls, used for horses only big sliding doors, armored cable is my first choice. I dont want any rats chewing wire, is this ok? I will be in Riverside county, Ca for this job. This is the best forum for questions and answers, something you can't get at Barns and Noble book store.
Top
#56223 - 09/17/05 09:20 AM Re: Armored cable in the Barn?
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
No typical armored cable is not OK.

The only armored cable allowed would be jacketed MC cable which looks like prewired liguidtight. It is not cheap.

UF cable (looks like NM) is OK but I would go with PVC conduit with PVC boxes.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#56224 - 09/17/05 09:59 AM Re: Armored cable in the Barn?
steve 2003 Offline
Member
Registered: 03/16/03
Posts: 9
Loc: san clemente, ca US...
Ok, looks like pvc with plastic boxes will do, the concern was stories I read about barn fires caused from metal boxes rusted from moisture with changing temperture's and animal waste the acid's speeding up the decay on metals, That would be great if there was a spray coating that could protect the armored cable like a rust proof application.
Now one point I wanted to make was the armored cable if out of reach like the ceiling runs, would that exception be possible? Ok Ok OK the secrect is out. I love armored cable, but I love horses also I want to be the safest first!
Top
#56225 - 09/17/05 11:46 AM Re: Armored cable in the Barn?
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9038
Loc: Estero,Fl,usa
Whats wrong with regular aluminum MC? It is wet location listed according to the box. I can see a grounding issue with plastic boxes if the connector doesn't have a bonding lug.
_________________________
Greg Fretwell
Top
#56226 - 09/17/05 12:16 PM Re: Armored cable in the Barn?
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
Nothing, except it is not allowed by 547.5(A)

Quote:
547.5 Wiring Methods.
(A) Wiring Systems. Types UF, NMC, copper SE cables, jacketed Type MC cable, rigid nonmetallic conduit, liquidtight flexible nonmetallic conduit, or other cables or raceways suitable for the location, with approved termination fittings, shall be the wiring methods employed. Article 398 and Article 502 wiring methods shall be permitted for areas described in 547.1(A).


I believe corrosion is the issue, notice only copper SE cable is allowed.

Notice the absence of RMC and FMC from the list.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 04/03/02
Posts: 6776
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 44 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals