The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Would ELV branch circuits be a good idea?
by LongRunner
Today at 07:42 AM
100% breakers?
by Texas_Ranger
Today at 06:13 AM
Forum Software Upgrade coming soon...
by Trumpy
01/14/17 07:11 PM
Faricating Guards out if Lexan?
by Trumpy
01/14/17 07:09 PM
Dangerous DIY Advice
by Potseal
01/12/17 09:52 AM
New in the Gallery:
Desk-mounted "power-board"
Shout Box

Top Posters (30 Days)
HotLine1 16
gfretwell 11
sparkyinak 10
ghost307 10
Trumpy 8
Who's Online
1 registered (HotLine1), 299 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#56058 - 09/13/05 10:18 AM Listed for use.
rad74ss Offline
Member

Registered: 04/19/04
Posts: 154
Loc: Pryor, OK USA
It has recently been brought to my attention by our welders that they have had trouble getting the plug from the welder to insert into the receptacle.

I took a peak at it (we are not supposed to do things outside of our job description) and this is what it looked like.

460 3 phase feeds into a fused disconnect. Immediately below the disco is a receptacle. The receptacle is rated at 120/208 3 phase Y. I look at the welder, it is set up for 460 1 phase. I look at the welders plug. It is 120/208 3 phase Y.

I told our welding guys that the plug and recept are supposed to be rated for the voltage being used. They then told me that every recept and plug for the 460 1 phase welders are set up the exact same way throughout the plant.

I was then told by another party that it was a maintenance issue and to go back to what I was doing.

The welding guys are now asking for the whole thing to be looked over by maintenance. Then phase C on a disconnect was malfunctioning. The screw could not be moved in or out. A fan connected to the disco along with the welder had its L3 wire laying (yes, laying) on the lug. When the guy doing the welding asked maintenance to fix it they told him to turn off the disconnect, pull the fuse, then re-insert the fuse with the wire pinned between the fuse and the fuse clip.

I told him not to do it and to to get maintenance to fix it. I also told him if they don't to talk to the Safety Supervisor.

I was looking for all code references to put in a letter to the Safety Supervisor about the welder situation and could use any help that could be offered. Right now one of our two electrical engineers (I being the other) is on medical leave so I have twice the work load plus having to train a new guy. I would appreciate any help.

Thanks,

Robert

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#56059 - 09/14/05 01:51 PM Re: Listed for use.
Redsy Offline
Member

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
110.3(A)(7)
110.3(B)
110.4

Note that the definition of "equipment" in Article 100 includes devices.

Top


ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals