#56043 - 09/13/05 04:44 AM Ungrounded Delta Service
Frank Cinker Offline
Member
Registered: 07/29/01
Posts: 311
Loc: Pennsylvania
In several of our local government buildings we have a 230V, 3Ph, 3W. electrical service. Measuring voltage to ground; A-G=230 volts, B-G=230 volts, C-G=0 volts. Why isn't there any voltage to ground on one phase?

[This message has been edited by Frank Cinker (edited 09-13-2005).]
Top
Work Gear for Electricians and the Trades
#56044 - 09/13/05 04:47 AM Re: Ungrounded Delta Service
winnie Offline
Member
Registered: 09/15/03
Posts: 649
Loc: boston, ma
Phase C is grounded. If this is supposed to be an ungrounded service, then there is a fault somewhere. But this is very likely 'corner grounded' delta rather than 'ungrounded' delta.

-Jon
Top
#56045 - 09/13/05 05:53 AM Re: Ungrounded Delta Service
HighPotter Offline
Member
Registered: 08/29/04
Posts: 42
Loc: So. Cal
Ungrounded systems are common in powerplants or substations. That way, IF one phase does become grounded, life goes on. Control of operations isn't effected.
Now a ground on a 2nd phase is another thing.

But I agree with Winnie. You most likely have a corner grounded system.If that is the case, your phase to ground reading is irrelevant.

HP
Top
#56046 - 09/13/05 08:21 AM Re: Ungrounded Delta Service
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9036
Loc: Estero,Fl,usa
That conductor should be white.
_________________________
Greg Fretwell
Top
#56047 - 09/13/05 07:51 PM Re: Ungrounded Delta Service
Larry Fine Offline
Member
Registered: 02/18/05
Posts: 693
Loc: Richmond, VA
You're so prejudiced!
_________________________
Larry Fine
Fine Electric Co.
fineelectricco.com
Top
#56048 - 09/13/05 08:36 PM Re: Ungrounded Delta Service
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9036
Loc: Estero,Fl,usa
The jokes just write themselves from there don't they.
_________________________
Greg Fretwell
Top
#56049 - 09/14/05 09:14 PM Re: Ungrounded Delta Service
wolfdog Offline
Member
Registered: 10/24/01
Posts: 135
Loc: Dallas,TX
I occasionally run into corner grounded delta in this area. It is rare and I have never gotten a good explanation for why that configuration appears in just one building in a neighborhood.
It seems to be old installations.

Anybody got a definitve answer?
Top
#56050 - 09/14/05 10:07 PM Re: Ungrounded Delta Service
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9036
Loc: Estero,Fl,usa
It is a very clean way to install 3p delta for motor loads if you don't need to serve 120v loads. You can use 2 pole equipment, one fewer service conductor and have 240v to run your motor on vs the 208 you get with wye.
Do you like "red leg" better? That comes with it's share of confusion too.
_________________________
Greg Fretwell
Top
#56051 - 09/15/05 06:08 AM Re: Ungrounded Delta Service
wolfdog Offline
Member
Registered: 10/24/01
Posts: 135
Loc: Dallas,TX
240 with a high leg is very common in this area.

Two of the 240 corner grounded delta have been on an elementary school and a private school that was formerly an orphanage. Both had small a\c loads - split systems and small rooftops -no chillers. Both systems served lights and receptacles.
3 pole main disconnect with a solid plug in the grounded phase. 3 wires in and 3 wires out.
Top
#56052 - 09/15/05 06:10 AM Re: Ungrounded Delta Service
Ryan_J Offline
Moderator
Registered: 08/19/03
Posts: 1374
Loc: West Jordan, Utah, USA
I think if this were an ungrounded system your measurement from phase "A" to ground and from phase "B" to ground would not be that close to each other. With an ungrounded system, the phase voltage to ground is erratic.
_________________________
Ryan Jackson,
Salt Lake City
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 61 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals