The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
1 registered (geoff in UK), 133 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#56043 - 09/13/05 04:44 AM Ungrounded Delta Service
Frank Cinker Offline
Member

Registered: 07/29/01
Posts: 317
Loc: Pennsylvania
In several of our local government buildings we have a 230V, 3Ph, 3W. electrical service. Measuring voltage to ground; A-G=230 volts, B-G=230 volts, C-G=0 volts. Why isn't there any voltage to ground on one phase?

[This message has been edited by Frank Cinker (edited 09-13-2005).]

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#56044 - 09/13/05 04:47 AM Re: Ungrounded Delta Service
winnie Offline
Member

Registered: 09/15/03
Posts: 652
Loc: boston, ma
Phase C is grounded. If this is supposed to be an ungrounded service, then there is a fault somewhere. But this is very likely 'corner grounded' delta rather than 'ungrounded' delta.

-Jon

Top
#56045 - 09/13/05 05:53 AM Re: Ungrounded Delta Service
HighPotter Offline
Member

Registered: 08/29/04
Posts: 41
Loc: So. Cal
Ungrounded systems are common in powerplants or substations. That way, IF one phase does become grounded, life goes on. Control of operations isn't effected.
Now a ground on a 2nd phase is another thing.

But I agree with Winnie. You most likely have a corner grounded system.If that is the case, your phase to ground reading is irrelevant.

HP

Top
#56046 - 09/13/05 08:21 AM Re: Ungrounded Delta Service
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
That conductor should be white.
_________________________
Greg Fretwell

Top
#56047 - 09/13/05 07:51 PM Re: Ungrounded Delta Service
Larry Fine Offline
Member

Registered: 02/18/05
Posts: 684
Loc: Richmond, VA
You're so prejudiced!
_________________________
Larry Fine
Fine Electric Co.
fineelectricco.com

Top
#56048 - 09/13/05 08:36 PM Re: Ungrounded Delta Service
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
The jokes just write themselves from there don't they.
_________________________
Greg Fretwell

Top
#56049 - 09/14/05 09:14 PM Re: Ungrounded Delta Service
wolfdog Offline
Member

Registered: 10/24/01
Posts: 135
Loc: Dallas,TX
I occasionally run into corner grounded delta in this area. It is rare and I have never gotten a good explanation for why that configuration appears in just one building in a neighborhood.
It seems to be old installations.

Anybody got a definitve answer?

Top
#56050 - 09/14/05 10:07 PM Re: Ungrounded Delta Service
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
It is a very clean way to install 3p delta for motor loads if you don't need to serve 120v loads. You can use 2 pole equipment, one fewer service conductor and have 240v to run your motor on vs the 208 you get with wye.
Do you like "red leg" better? That comes with it's share of confusion too.
_________________________
Greg Fretwell

Top
#56051 - 09/15/05 06:08 AM Re: Ungrounded Delta Service
wolfdog Offline
Member

Registered: 10/24/01
Posts: 135
Loc: Dallas,TX
240 with a high leg is very common in this area.

Two of the 240 corner grounded delta have been on an elementary school and a private school that was formerly an orphanage. Both had small a\c loads - split systems and small rooftops -no chillers. Both systems served lights and receptacles.
3 pole main disconnect with a solid plug in the grounded phase. 3 wires in and 3 wires out.

Top
#56052 - 09/15/05 06:10 AM Re: Ungrounded Delta Service
Ryan_J Offline
Moderator

Registered: 08/19/03
Posts: 1355
Loc: West Jordan, Utah, USA
I think if this were an ungrounded system your measurement from phase "A" to ground and from phase "B" to ground would not be that close to each other. With an ungrounded system, the phase voltage to ground is erratic.
_________________________
Ryan Jackson,
Salt Lake City

Top