The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#55779 - 09/06/05 01:14 PM transfomer taps
jtorres Offline
Junior Member
Registered: 09/05/05
Posts: 6
Loc: San Antonio, Texas
Hello everybody
I`m new to this site and what I`ve seen so far I think this is a great forum.

I was having a discussion with another student of the trade and we couldn`t agree on the following statement.
" Taps are usually provided on the secondary low-voltage side at 2 1/2 percent incraments to correct the phase angle of the secondary voltage"
Would you`ll say that this is a true or false statement?
Top
Work Gear for Electricians and the Trades
#55780 - 09/06/05 01:32 PM Re: transfomer taps
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
I thought they where there to dial in the secondary voltage if the primary voltage consistently runs high or low.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#55781 - 09/06/05 02:01 PM Re: transfomer taps
Alan Nadon Offline
Member
Registered: 03/10/05
Posts: 398
Loc: Elkhart, IN. USA
Answering off the top of my head. (In this group a good way to lose your head.) I think the answer for the test would be False. The taps are for voltage not angle of phase.
A transformer is rated with a fixed primary voltage which is not always available. that is 480 delivered by the utility may be 470 or 490 volts. If you want 240 on the secondary you would use the taps to get 240 volts. Make Sense ?
Alan--
Looking again I just repeated what Iwire said.

[This message has been edited by Alan Nadon (edited 09-06-2005).]
_________________________
Alan--
If it was easy, anyone could do it.
Top
#55782 - 09/06/05 02:49 PM Re: transfomer taps
jtorres Offline
Junior Member
Registered: 09/05/05
Posts: 6
Loc: San Antonio, Texas
Thanks guys for the quick response and clearing this up for us.
Top
#55783 - 09/06/05 05:59 PM Re: transfomer taps
winnie Offline
Member
Registered: 09/15/03
Posts: 652
Loc: boston, ma
For low voltage distribution transformers (eg. 480V delta to 208V/120 wye), is it more common to see the taps on the primary or secondary side?

I was under the impression that taps were often on the primary side, so that the core would not be excessively saturated if the supply voltage was a tad high. But I don't have a large sample of transformers to go by.

-Jon
Top
#55784 - 09/06/05 06:06 PM Re: transfomer taps
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
Jon

Quote:
is it more common to see the taps on the primary or secondary side?


Much more common to see the taps on the front side.

Sorry....

Seroiusly I have not paid that much attention to remember if the taps are primary or secondary.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#55785 - 09/06/05 06:28 PM Re: transfomer taps
hypress Offline
Member
Registered: 07/20/04
Posts: 132
Loc: Charleston WV
Taps are on the primary side. If your voltage is low you need to select a lower voltage tap (take some of the primary winding out of the circuit). If your voltage is high you need to select a higher voltage tap (add some primary winding to the circuit) It is just the opposite of what you think you would do . It's all about turns raito. If you have a chance to look at a high voltage transformer like 13200/480V it should have a nameplate with a diagram it will be easy to see what is happining with the primary taps.
Top
#55786 - 09/06/05 09:42 PM Re: transfomer taps
frenchelectrican Offline


Member
Registered: 02/06/03
Posts: 938
Loc: Wi/ Paris France { France for ...
any transformer 35 KVA or larger useally have a primary tap in the front and it will marked 4 points above and 2 points below but some have more than that so double check the nameplate to make sure

i do check transformer lead both " unloaded and loaded to make sure it correct voltage most of my time i set at least one step above the normal voltage by time it loaded up it get to correct level

Merci , Marc
_________________________
Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)

Top
#55787 - 09/07/05 03:52 AM Re: transfomer taps
jtorres Offline
Junior Member
Registered: 09/05/05
Posts: 6
Loc: San Antonio, Texas
Taps can also be on the low side. You can have one primary voltage and taps for different out-put voltages. But can we all agree that taps Do Not correct the phase angle of the SECONDARY voltage?
Top
#55788 - 09/10/05 08:04 PM Re: transfomer taps
WFO Offline
Member
Registered: 09/03/05
Posts: 206
Loc: Cat Spring, TX
Quote:
"But can we all agree that taps Do Not correct the phase angle of the SECONDARY voltage?"

That is correct, taps are for voltage adjustment, NOT phase angle or power factor correction.
Top
Page 1 of 2 1 2 >

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Members: Non-Members: Did you know?
by Admin
01/22/17 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM
International Wire Colour Codes
by Texas_Ranger
01/21/17 03:29 PM
Looking for older post
by Texas_Ranger
01/21/17 03:22 PM
Last time to chat here
by Trumpy
01/20/17 11:41 PM

Who's Online
3 registered (gfretwell, TRUE POWER, Admin), 123 Guests and 12 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Tom
Tom
Member Since: 01/01/01
Posts: 1069

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals